Quick outdoor electric question

Rosco

Well-known member
Joined
Jan 4, 2009
Messages
1,140
Location
South Georgia
I am installing a paver patio with 2 light post. I plan on running 12-2 outdoor wire inside of 3/4 electrical conduit from my shop. It will be buried and run inside of a concrete footer for the outdoor fireplace. I plan on using all outdoor rated materials for the outlet and light switch.

Anyone see any issues with this plan? I know there are issues with insulated wire inside of conduit, but just wondering about my plans. I am hoping the 3/4 inch will provide protection and be large enough not to cause any issues with the wire.

Thanks in advance!
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
12-2 w/grd UF, any UF for that matter is darn difficult to pull thru conduit, especially PVC conduit. Use lots of lube and have someone pushing while you pull the fish tape. Or as noted, just use individual wires.

Be sure and use WR rated GFCI receptacles. They will be marked as such right on the front of them.
 
OP
R

Rosco

Well-known member
Joined
Jan 4, 2009
Messages
1,140
Location
South Georgia
Thanks, i have pulled it before (pain) and plan on doing it one 10' section at a time. Installing the wire as i put the conduit together. Thanks for the tip on the receptacles!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Do the smart thing, leave the UF on the shelf use THWN conductors in the PVC, the PVC needs to be installed as a complete system then pull conductors to be compliant w/ code requirements.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,276
Location
Modesto, CA
Thanks, i have pulled it before (pain) and plan on doing it one 10' section at a time. Installing the wire as i put the conduit together. Thanks for the tip on the receptacles!

Thats a bad idea. The glue could damage the insulation.

Why make things harder on youreself than they have to be. Glue the conduit together running a pull string through as u assemble the sections and then use THWN and be done with it!
 
OP
R

Rosco

Well-known member
Joined
Jan 4, 2009
Messages
1,140
Location
South Georgia
Looks like THWN might be the way to go. Definitely want to be in code as I have a lot invested in all my other projects being in code. Was not aware that UF was not code compliant, or maybe the way I was going to join the pvc is not code, either way Thanks!!
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,276
Location
Modesto, CA
Looks like THWN might be the way to go. Definitely want to be in code as I have a lot invested in all my other projects being in code. Was not aware that UF was not code compliant, or maybe the way I was going to join the pvc is not code, either way Thanks!!

Wait backup. No one said UF is not code compliant in conduit. UF-b and NM-b most definitely can be ran in conduit. Its just a PITA and therefore not advisable!

Whats not code compliant is running the wire through the conduit as u glue it. Norcal already pointed this out. Next time try to read more carefully!
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,372
Location
Michigan
The reason that you don't want to install the wire as you run the conduit is so you could replace the wire in the future, imagine trying to pull a bunch of UF cable out and replace it after everything is together.

Sent from my SM-G900V using Tapatalk
 