Question: can you put 2 grounds on the same ground bar in the pannel?
(ie) 2 green wires in the same slot (I don't know what it's called?)
(ie) 2 green wires in the same slot (I don't know what it's called?)
Question: can you put 2 grounds on the same ground bar in the pannel?
(ie) 2 green wires in the same slot (I don't know what it's called?)
So if I put 2 #12AWG under one Screw and 1 #10AWG under it's own screw On the Ground Bar I would still be in complience with code?
Marc...
So if I put 2 #12AWG under one Screw and 1 #10AWG under it's own screw On the Ground Bar I would still be in complience with code?
Marc...
Again, it depends on the panel. Read the label inside the door. It will list how many wires, of what sizes are allowed in each ground and neutral hole, and specify the torque for them. This is your clue as to whether the panel allows multiple wires on one ground bar position.
See the pic for an example.
![]()
Charles
So If I understand you right? I can have a (2) or (3) 14 to 10 AWG grounds under the same screw? My pannel has the same information as what is listed in you attached picture But I should match 14 with 14 , 12 with 12 and 10 with 10? Inother words don't mix 10AWG with 14AWG, or is this acceptable?
I would have absolutely no problem mixing them under the specification of that label.