Quick question on breakers . . .

ckadams00

Well-known member
Joined
Sep 12, 2011
Messages
1,273
Location
Seattle, WA
I am going to wire some additional shop lights in my basement shop and was checking the panel and breakers to see if I had any capacity issues. It sia Square D panel with QO breakers. Here is the thing - EVERY breaker in the panel is 10A. I've read a lot of places that the dryer, dishwasher. etc should be at least 20A. What gives? We never have breaker problems except on one breaker at Christmas time when we put a lot of lights on one circuit.

Is this because we have an old house and probably older wiring? Or is the 20A suggestion just overkill?

Is there any way to tell the wire gauge without calling an electrician? I'm not comfortable pulling any covering off the breaker panel just to find out.
 
To avoid these ads, REGISTER NOW!

chickenhauler

Well-known member
Joined
May 31, 2011
Messages
473
Location
Pennsylvania
I'm all for DIY, but if you're not comfortable taking the cover off the breaker box, then you should call a professional.
 

71flh

Banned
Joined
Jun 15, 2011
Messages
379
Typically, in the US there's no such thing as a 10A breaker in a house. Lighting circuits using 14AWG wire use 15A breakers, and utility circuits using 12AWG wire have 20A breakers.
 

Thruxton

Well-known member
Joined
Dec 30, 2010
Messages
767
Location
Virginia
Take a closer look. What you are seeing is the 10KV rating printed on the body of the breaker below the switch handle, not the breaker's amperage capacity, which is molded into the end of the handle (and harder to see on old breakers).
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Take a closer look. What you are seeing is the 10KV rating printed on the body of the breaker below the switch handle, not the breaker's amperage capacity, which is molded into the end of the handle (and harder to see on old breakers).

There is no "10KV" rating on there, there is a 10,000 AIC rating or 10 KAIC rating on some breakers (AIC = Amperes Interrupting Current), 10 ampere breakers are a standard size, there was talk about installers using 10A breakers to "get around" AFCI requirements instead of 15A before AFCI's were expanded to just about everything in a residence.It was a shaky way to weasel out of it.......
 
OP
C

ckadams00

Well-known member
Joined
Sep 12, 2011
Messages
1,273
Location
Seattle, WA
Man I love this website!:thumbup:

Thanks guys for the response - I realize this is a "duh" question for most of you but I didn't see the little numbers printed into the switch toggle and couldn't for the life of me understand why every breaker in the house would be 10A.

Sometimes the littlest detail causes the biggest questions.

Just redid the map of my panel - lots of "15s" "20s" and a 30A for the A/C.

Thank You!
 

Thruxton

Well-known member
Joined
Dec 30, 2010
Messages
767
Location
Virginia
There is no "10KV" rating on there, there is a 10,000 AIC rating or 10 KAIC rating on some breakers (AIC = Amperes Interrupting Current), 10 ampere breakers are a standard size, there was talk about installers using 10A breakers to "get around" AFCI requirements instead of 15A before AFCI's were expanded to just about everything in a residence.It was a shaky way to weasel out of it.......

I stand corrected. I took a look at the topic more closely and learned something new- thanks!
 