Quick questions for the electricians in the group:

Wiring a 12 KV electric unit heater. I understand that I need #4 copper from 70amp 2p breaker. What is the wire gauge needed for the associated ground? Can I use #8?

Will I need 1 inch greenfield for that run of wires or can I fit it in 3/4 inch?

Thanks up front -- I appreciate the shared knowledge!
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA
Quick questions for the electricians in the group:

Wiring a 12KV electric unit heater. I understand that I need #4 copper from 70amp 2p breaker. What is the wire gauge needed for the associated ground? Can I use #8?

Will I need 1 inch greenfield for that run of wires or can I fit it in 3/4 inch?

Thanks up front -- I appreciate the shared knowledge!
I assume you meant 12KW... you need 62.5a rated wire.... so #6 THWN will work (good for 65a).... ground wire would need to be #8...

might be kinda tight fitting that in 3/4"... i would go with 1"
 
OP
O

olytdi

Well-known member
Joined
Dec 3, 2011
Messages
2,202
Location
Olympia, Washington
Thanks Wylie! Yes! I meant KW! LOL.

I thought it was #4 -- #6 just means more savings! Thanks for confirming the #8 ground and the greenfield size!
 
OP
O

olytdi

Well-known member
Joined
Dec 3, 2011
Messages
2,202
Location
Olympia, Washington
3/4" greenfield is fine. NEC limit is four #6 thhn in 3/4". I assume this is a short whip?

So the manufacturer's website states #4 for this heater and a 70 amp 2p breaker. Any idea why that differs from the recommendation here? I already have the breaker -- 70 amp would require the #4 wire correct? I think that they're accommodating the 80% rule(?).
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,066
Location
Modesto, CA
So the manufacturer's website states #4 for this heater and a 70 amp 2p breaker. Any idea why that differs from the recommendation here? I already have the breaker -- 70 amp would require the #4 wire correct? I think that they're accommodating the 80% rule(?).
12KW / 240v is 50a. 50a x 125% = 62.5a wire.... #6 is good for 65a but the manufacturer is basing their wire size off breaker size.... 65a breaker is not a standard size and code allows you to use the next standard size as long as the load doesnt exceed the wire rating, which it wont....
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,028
Location
NJ
So the manufacturer's website states #4 for this heater and a 70 amp 2p breaker. Any idea why that differs from the recommendation here? I already have the breaker -- 70 amp would require the #4 wire correct? I think that they're accommodating the 80% rule(?).
The conductor ampacity needs to be 50a x 125% = 65A.
Mfr probably assumed worst-case use of 60C rated wire (NM-B) and #4 copper is good for 70A.
If you use THHN/THWN, rated for 75C (in this case) #6 copper is good for 65A.
The 70A cb can be used in either case.
 
OP
O

olytdi

Well-known member
Joined
Dec 3, 2011
Messages
2,202
Location
Olympia, Washington
The conductor ampacity needs to be 50a x 125% = 65A.
Mfr probably assumed worst-case use of 60C rated wire (NM-B) and #4 copper is good for 70A.
If you use THHN/THWN, rated for 75C (in this case) #6 copper is good for 65A.
The 70A cb can be used in either case.
Okay, thanks! What I hear you saying is that for 12000 watts, I can use #6 THHN/THWN and use a 70 amp breaker.
 
OP
O

olytdi

Well-known member
Joined
Dec 3, 2011
Messages
2,202
Location
Olympia, Washington
12KW / 240v is 50a. 50a x 125% = 62.5a wire.... #6 is good for 65a but the manufacturer is basing their wire size off breaker size.... 65a breaker is not a standard size and code allows you to use the next standard size as long as the load doesnt exceed the wire rating, which it wont....
Okay, thanks! What I hear you saying is that for 12000 watts, I can use #6 THHN/THWN and use a 70 amp breaker.
 