480 primary and 120/240 secondary.

is there any issue with having a load on the 240 x1/x4 while still pulling a load on the x2/x3 and x4 for 120? assuming that both 240 and 120 loads combined are a max of 17.5 amps and the transformer is 40/20 amp rating for the kva and load outputs?
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,758
Location
SE Michigan
If its something like 240vac "power" and 120vac "controls" for a specific machine, then probably fine, minimal amp draw on 120vac.

I would not try that for stationary/lighting/etc loads.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
You need to be concerned with the load on a per winding basis to be sure there is no overload condition. Specifically, is x3-x4 overloaded from the two loads thru it. Need the kva rating of the xformer, nameplate would be best and can then calculate if issue. Need overcurrent protection for each ckt on the secondary and also primary.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
Also x2-x3 should be bonded to equipment ground and neutral comes off of x2-x3.
 
OP
K

Kracin

Well-known member
Joined
Mar 25, 2013
Messages
1,666
Location
Omaha, NE
If its something like 240vac "power" and 120vac "controls" for a specific machine, then probably fine, minimal amp draw on 120vac.

I would not try that for stationary/lighting/etc loads.

the main load is for a 7.5 amp ultra drive, second 120v load is for a lift table pulling 10 amps,

You need to be concerned with the load on a per winding basis to be sure there is no overload condition. Specifically, is x3-x4 overloaded from the two loads thru it. Need the kva rating of the xformer, nameplate would be best and can then calculate if issue. Need overcurrent protection for each ckt on the secondary and also primary.

its a 5kva transformer, and both loads aren't constantly being used, the main 240 load is mostly used, the second 120v load is only used mometarily every 10-20 minutes.

when i went through it in my head at the time it sounded fine, just wanted to double check and im not at work anymore with time to sit down and read through it.

worse comes to worse, i'll just swap the transformer for a larger one to accommodate, but only pulling 1/4 of the load on the 120 side and less than 1/2 of the load on the 240 side seemed like it would be fine.

Also x2-x3 should be bonded to equipment ground and neutral comes off of x2-x3.

yes, thats how you get 120 off of the secondary vs using x1-x4 for 240 secondary power
 