I understand the idea behind sizing wire due to voltage drop. But is the end result so you maintain 120 volts at the end of the line?

Here's where I'm coming from with this question - while poking around in the basement tonight I was looking at a 15amp circuit that appears to only feed four outlets on the opposite corner of the house. It's 14-2 wire but because of the way the wire is routed its probably about 80 feet from the panel to the last outlet. I believe rule of thumb is about 50' for 14-2?

Anyway - I put the meter on it and I'm getting 120.7 volts off that last outlet. First outlet is slightly more but it's only about 12 feet from the last outlet.

Voltage coming into the house is always in the 121-123 range - so wondering if this should be of any concern? I've actually had a computer plugged into this circuit for some time now so I'm thinking I'm cool. Thanks for any input.
 
To avoid these ads, REGISTER NOW!

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
All depends on the load you put on it. 14-2 @150 feet won't drop much with a 1 amp load. At a 10 amp load, different story. Your computer probably draws 2-3 amps, so not much voltage drop.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
As Alchymist stated, voltage drop is dependent on load. The more load you put on the circuit, the more voltage drop you will get from the resistance of the wire.
With no load on the circuit, you can expect to measure near 120v even beyond the recommended length, but with near maximum load, you will be getting voltage drop.

If you are really concerned, put a heater or other heavy use device on the end of the circuit, and measure the available voltage with that load.
 
To avoid these ads, REGISTER NOW!

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
Almost every computer made has a switching power supply that works on a range of voltages. Typically, the minimum voltage on a 120v supply is 100V.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,894
Location
oregon
As Alchymist stated, voltage drop is dependent on load. The more load you put on the circuit, the more voltage drop you will get from the resistance of the wire.
With no load on the circuit, you can expect to measure near 120v even beyond the recommended length, but with near maximum load, you will be getting voltage drop.

If you are really concerned, put a heater or other heavy use device on the end of the circuit, and measure the available voltage with that load.

X2 on this. Check the voltage under load.

lg
no neat sig line
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,289
Location
SE MI
Most voltage drop calculators work on percent voltage drop, under load, at the end of the wire. 3-5% is acceptable. 7% is pushing it. 5% of 120V is 6V (114V), but again, you can only accurate measure this at load.

You can run a 10A load over 100' of 14 gauge copper wire and still have less than a 5% voltage drop.
 
OP
R

rvr6000

Well-known member
Joined
Oct 3, 2010
Messages
1,072
Location
St. Paul, MN
Thanks for the help, guys. I guess I didn't know it had to be under load to accurately measure the drop. Will try that tonight.
 

eljefino

Well-known member
Joined
Feb 21, 2008
Messages
336
Also your meter might be somewhat inaccurate measuring "true" AC. Wander from outlet to outlet measuring it and try to get representation from both phases.

From the power plant to the transformer to the meter, fusebox, outlet, and appliance power supply there are a series of (semi-) BS factors for loss. Where you really start having issues is when you break out the 16-18 AWG extension cord and then put a 1500 watt heater on it. As said above your computer will be fine; they take all sorts of brownouts in stride. It's those 1/2 second blackouts that mess my electronics up.
 
To avoid these ads, REGISTER NOW!