I've seen a lot of mixed messaging regarding VFDs on older motors. If the motor isn't being asked to do anything outside of it's normal operation range (no running at half speed etc) is there really all that much danger?
the "issue" is VFD's don't make a sine wave, they approximate it by chopping DC bus voltage which is about 1.4x the "line" voltage. so if you see 240V RMS on your meter, the motor windings will see 330V. granted they're technically seeing that anyways (Peak to peak voltage is higher than RMS). the problem is the harmonics from the PWM action. the longer the wires between the VFD and the motor, the higher those spikes can stack. if you put a motor on a VFD, keep it close.
we have a LOT of motors at work that aren't listed for VFD use, running just fine for YEARS. And i'm not talking about 'i've had my toy with a VFD on it that gets used once a month for 20 minutes' years, I'm talking '24/5, turn it on monday, turn it off friday, no stopping' hours.
I doubt whatever you're planning is going to hit those hours.
other VFD benefits:
it's a soft starter if you set the acceleration time right. great for not dimming your neighbors lights, and having them call the power company to complain, then the power company showing up at your door and reminding you you're not allowed to DOL start motors over 5hp on your service.
VFDs generally will tell you WHY they error out, especially if you put in the right motor data. overloaded motor? VFD will shut it off and let you know why it stopped.
running half speed isn't a problem if you've got the cooling to match. if you aren't sure, hook up the temp sensor that's in most bigger motors to the VFD, and tell it to stop if it trips.
This is my new compressor at work. 10hp. came with a VFD. runs down to 30Hz before it shuts off. it starts unloaded, except when it doesn't. VFD has no problem getting it to turn over with 150PSIG in the aftercooler.
motor is rated SF 1.15 @ 60Hz, 1.0 @ 50Hz. 10HP at both frequencies. cooling fan looks tiny to me but I can hold my hand on it after it's been running for 100 hours straight so it must be fine.
Some good discussion of VFD use on older motors here:
I just got a bridgeport with a J head "pancake motor- built in 1954. I was thinking ov using a TECO FM 50 to power it. Does the old insulation present a problem- or a possible problem? I have read the early VFDs had voltage spikes leading to concerns. How are the newer VFD's? (I do plan on...
www.practicalmachinist.com
Getting a smaller pulley that takes 20% or so of the load off the motor to give it a bit more thermal headroom might be prudent if I chose to run the existing motor on a VFD.
I need to think about this more, but the fact that the motor in question is a dual voltage unit might be helpful in this case. Since it was designed to hold 460V and not just 230V it should have been specced to a higher standard insulation wise.
that's not the data you need to look at. a dual voltage motor's windings never see more than 230V. at 460V they're just running in series. you want to look at the class of insulation. motors that run on VFDs tend to have higher rated insulation, and they often do a better job of gluing the windings together to prevent vibration from the VFD's carrier frequency.
Here's our shop's QR-25.
It's very old. ran alot before the new compressor showed up. found out it wasn't unloading properly (probably for years). fixed that. now it runs when I do maintenance on the new one.