Raceway for Electic in concrete foundation

ckrzysko

Member
Joined
Mar 11, 2014
Messages
14
Hello all -I would like to conceal the electric coming into the garage. Can I use 1-1/4 in. Rigid 90-Degree Steel Conduit Elbow (heavy wall conduit) and stub above the foundation wall, so the electric service is coming up the 2x6 wall? Naturally I will have to position it so the service comes up through the concrete inside the wall and where the panels is going to be. Also the service coming through the wall is about 26 inches below grade.

Heavy wall.jpg
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
It is very common to install conduit stubups into concrete. Is there a reason you think you need a steel 90 rather than a pvc 90?
 
OP
C

ckrzysko

Member
Joined
Mar 11, 2014
Messages
14
It is very common to install conduit stubups into concrete. Is there a reason you think you need a steel 90 rather than a pvc 90?

For a few bucks more, I would rather overkill and make sure it pass inspection. From the outside I would use schedule 80 to the heavy wall and then connect to the poly that is buried.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
For a few bucks more, I would rather overkill and make sure it pass inspection. From the outside I would use schedule 80 to the heavy wall and then connect to the poly that is buried.

I can assure you, pvc conduit will pass inspection. There is no reason to use steel just because it's in concrete.

Second, what kind of conduit are you using that you're calling poly?
 
To avoid these ads, REGISTER NOW!

Elginz

Well-known member
Joined
Dec 29, 2014
Messages
431
Location
Oconto, WI
Use PVC, it is non-conductive, will never rust, easier to work with (fittings, smooth inside for wire pulling), fairly cheap, on and on.

Just my opinion.
 
OP
C

ckrzysko

Member
Joined
Mar 11, 2014
Messages
14
I can assure you, pvc conduit will pass inspection. There is no reason to use steel just because it's in concrete.

Second, what kind of conduit are you using that you're calling poly?

High Density Polyethylene (HDPE) Conduit
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Depending on where youre at and your weather I'd personally bring the pipe up out of the ground and install an expansion joint before lb'ING it into the building/back of panel,unless you're bringing it in below the frost line.
I've seen plenty of pipes snapped off from ground heaving while building didn't move at same rate.
 