Radiant Floor Heating System Repair

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
I just discovered that my 18 yr old radiant floor heating system is not working and so I am looking for the parts to rebuild it. This is for my 450 sq ft garage/shop. I basically designed this myself back in 2006. Three circuits of 1/2" pex (~485 ft total) in the slab and they feed into two shared headers so it is effectively one closed loop. Cryo-tek antifreeze is the fluid so the heater core won't freeze when the system is off and it is cold outside. The two 3/4" pipes going into the wall are capped off in the attic so they don't do anything. I had originally built it with one 1/25th hp Grundfos pump but found that was not enough flow rate so a 2nd identical pump was put in series and it has worked like that for 18 years. I am not sure if it is the Takagi heater that is the issue or if the impeller blades are gone. Both pumps sound/feel like they are working when it turns on but the heater does not fire. I am going to replace the tankless heater and the pumps. I'd like to get just one bigger pump but I am unsure what size single pump is equivalent to the two 1/25 hp pumps in series. Is it as simple as 2/25 hp or a 1/12 hp single pump? Menards has 1/6 hp three speed pumps that would seem to work fine since I could use whichever speed gives the best flow rate but these 1/6 3 spd pumps are quite spendy. Picture was taken in 2006 when I had just completed the system.

So should I look for 1/12 hp pump, a 1/6 hp 3 spd pump, or just replace them with two 1/25 hp in series like it has always been?

1728131697672.jpeg
 
Last edited:
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,974
Location
Peace Valley,mo
Have you even checked the ph or checked the temperature the what the mix is good for or added inhibitor? Parallel pumps pick up about 80% of gpm head goes up some.
Pump manufacturer has all that info. Propylene glycol has to be at 30% or more for the inhibitors to work correctly. Under 30% prop glycol can turn to garbage in a heart beat. The three valves to the left of the pumps with water hose adaptors would be a great place to back flush.

 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
The antifreeze was replaced about 4 or 5 years back and I believe I added about 30% water so it is roughly a 70/30 mix. I used no inhibitor - I need to learn more about what that is and how to use it. The PEX tubing says oxygen barrier so what I have been reading is that I can go with a cast iron pump which is cheaper than the bronze choice. I turned on the power to the pumps again just now and it seems like they are both seized so my guess is the pumps are the issue here and maybe not the heater.

The two 1/25 hp pumps here are in series with each other.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,957
Location
Rhode Island
Before shotgunning thousands of dollars of new pumps and a boiler, why don't you do some basic trouble shooting first?

See if the boiler has any error codes. See if the flow switch is being made. Check or replace the igniter.

Are pumps in series ever good science? Seems the few multiples I see are in parallel.

jack vines
If your issue is not enough head pressure, two pumps in series will more or less double the maximum head pressure at a given flow rate. Normally you'd buy a "two stage" pump that internally has one impeller feeding another, but you can do it with separate pumps too.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Before shotgunning thousands of dollars of new pumps and a boiler, why don't you do some basic trouble shooting first?

See if the boiler has any error codes. See if the flow switch is being made. Check or replace the igniter.

Tankless heater has no codes it just shows there is no flow. Could be the flow sensor. I will start with the pump(s) replacement and if it fires up then good. If not I will put in a new heater they are not really expensive certainly not as much as a boiler.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
If your issue is not enough head pressure, two pumps in series will more or less double the maximum head pressure at a given flow rate. Normally you'd buy a "two stage" pump that internally has one impeller feeding another, but you can do it with separate pumps too.
Cool that is how I was kinda thinking how two in series would work - about 2x the force on the fluid. I think I ended up being lucky with the two smaller pump models I happened to buy at the time and it ended up being an alright flowrate ~2.3gpm for the heater. I am looking at the Grundfos UP pump specs now to see what head pressure with the two pumps comes out to ~2.3gpm and if another single pump would be in the same spec range. Thanks
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,974
Location
Peace Valley,mo
The antifreeze was replaced about 4 or 5 years back and I believe I added about 30% water so it is roughly a 70/30 mix. I used no inhibitor - I need to learn more about what that is and how to use it. The PEX tubing says oxygen barrier so what I have been reading is that I can go with a cast iron pump which is cheaper than the bronze choice. I turned on the power to the pumps again just now and it seems like they are both seized so my guess is the pumps are the issue here and maybe not the heater.

The two 1/25 hp pumps here are in series with each other.
70% glycol is way to much it is killing the efficiency of the pumps and heat transfer. It's harder to pump as the percentage goes up. Any chiller/ boiler glycol has two % charts. One is total protection the other is temperature that it slushes and still protects the equipment.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,957
Location
Rhode Island
Tankless heater has no codes it just shows there is no flow. Could be the flow sensor. I will start with the pump(s) replacement and if it fires up then good. If not I will put in a new heater they are not really expensive certainly not as much as a boiler.
Shotgunning pumps in there is a waste of money, too, if that's not the problem.

What model is the heater? A new flow switch could be as cheap as $30 if that is the issue.
 
To avoid these ads, REGISTER NOW!
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
70% glycol is way to much it is killing the efficiency of the pumps and heat transfer. It's harder to pump as the percentage goes up. Any chiller/ boiler glycol has two % charts. One is total protection the other is temperature that it slushes and still protects the equipment.
How did I misread the glycol level requirement? It can often hit -25*F here in Minnesota and the tankless water heater heat exchanger is basically directly exposed to the outside temps with a ~10" exhaust vent.

1728227204122.png
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Shotgunning pumps in there is a waste of money, too, if that's not the problem.

What model is the heater? A new flow switch could be as cheap as $30 if that is the issue.
I think you missed my mention yesterday when I tried powering on the circulator pumps and there was no pump sound just a noticeable hum from the power being applied.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,974
Location
Peace Valley,mo
How did I misread the glycol level requirement? It can often hit -25*F here in Minnesota and the tankless water heater heat exchanger is basically directly exposed to the outside temps with a ~10" exhaust vent.

1728227204122.png
Radiate floor systems hold so little volume 450' 1/2" pex hold 4.15 gallons and may be another 2-3 for pump, boiler and piping. 70% is good.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,035
Location
West central Indiana
Are you sure the loop actually has fluid in it? Those cartridge circulators are generally pretty reliable.
I have heard of quite a few locked up if left setting without being exercised over the summer.

Many of the pump controllers have a "pump exercise" feature now that runs it for a period of time. My calleffi runs the pumps for 30 seconds every 72 hours
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,410
Location
N CA
After checking the ph, if you can figure out how to connect it, get a fresh water hose connected to the WH and see if city pressure and good flow fires the unit. This would be simple if you had the tankless iso valves, but it is worth doing anyway. As to the cost effectiveness of a boiler vs another takagi, consider the additional benefits the boilers offer. One you get a circulator built into the boiler, which simplifies your primary secondary piping. As well, you get outdoor reset control which simplifies the wiring and can get the best out of your system. Also they are pretty much all 95% vs your 80 on the water heater.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Last week I found and replaced the 10uF capacitors in the two Grundfos pumps and after that there was no difference - tankless heater did not fire. Friday afternoon I went to try it again powered on the heater, waited a minute and then turned on the pumps and the heater fired up like normal and has been working properly since then. I did order and have here a replacement flow sensor for the old Takagi T-KJr if it stops working again that is most likely the issue I think.

I will be going to Menards tomorrow to get some PH test strips to see how the fluid is.
 
OP
5

59ctd

Well-known member
Joined
Apr 1, 2006
Messages
78
Location
Lakeville, Minnesota
Here is the test result that I got this morning. To me the ph looks like it is way on the 'OK' end of the range according to the color gauges on the side of the bottle.
1729090433952.jpeg
 

gerry.pom

New member
Joined
Jan 30, 2020
Messages
3
Location
Thunder Bay
I've used Grunfoss 15-58 pumps for radiant heat in houses much larger than your garage with no issues and some with glycol 30%.
But always with primary/secondary piping arrangement. Some boilers have a built in primary pump others don't. In that case I'll use two 15-58 pumps. Pretty much all boiler manufacturers recommend primary/secondary loops
 