"code" is the difference.
There are TINY differences between the two. NONE will effect the performance or reliability of the unit.
The 'tweeks' were required in order to make code officials 'happy' I have many of these seisco units used in floor heat applications. The ONLY modification is swapping out of the hi limit switch.
BOTH RA-9 and SH-9 have TWO 4500 watt elements
4500 watts / 240 Volts = 18.75 amps x 2
My Guess is they combine the elements onto ONE circuit.
ONE 40 amp Breaker or ONE 50 amp Breaker Will work just fine.
I would however be sure to use the gauge of wire recommended by code to handle 40 or 50 amps to make sure you are safe.
You cannot go wrong putting in a 50 amp breaker and wire capable of handling 50 amps.
I did have one unit with a 'weak' breaker that after time if the unit was running continuous for a while would trip the breaker. Breakers are controlled by heat. Continuous amps running through the breakers will heat them up and so trip them. Generally you would NOT use a "hot water heater" continuously for 2-3 hours like in a floor heat application. Doing so you would build up more ambient heat through long term usage. 2x18.75 amps is close to the full 40 amps. You would probably avoid any problems by using a 50 amp.
I have NEVER purchased anything smaller than an RA-14. They require TWO Circuits
7000 W / 240 Volts = 29.2 Amps ONE 30 amp breaker works but I have had problems like I said with 'weak' ones.
PERSONALLY, If it was me I would purchase the RA-14, TWO reasons.
#1 you will have TWO circuits to break down the load. Smaller wire Costs LESS.
#2 With these units you will spend the EXACT SAME amount of money to run an RA-09 running at Max output as to use an RA-28 only running at a fraction of capacity. ZERO difference. The only noticeable change will be how quickly the unit recovers, and how often it runs. If you have a noisy pump you will appreciate the unit recovering as quickly as possible. Plus it would save wear and tear on ALL the parts of the system.
Both units will require the exact same BTU s 3400 btu's per KW. So weather you put them in all at once or over time it costs the same.
AND the price difference is ONLY $50. You MAY save that on wire if you are running it a ways from the breaker panel.
The ONLY reason NOT to would be if you are already maxing out your amp draw for the panel. THEN and only then would I choose the RA-09.
Build in a Safety factor with the RA-14 you will NEVER regret it.