Okay, so I have an electric radiant heat panel on the way for my shop and want a sanity check.
The boiler is an electric unit rated at 12KW (240V). The literature lists a maximum 50A draw. They specify a 70 amp double-pole breaker and 4 gauge copper wire.
My problem/question is with the 4 gauge wire and what options I have. I have 2" conduit running out the top of my service panel into the attic over the shop. The wire will exit the conduit, cross the attic, then drop down through an interior wall into the closet/bathroom where the radiant heat panel will be mounted. The total run going up, across and down will be approximately 50ft.
As best I can tell my options are finding 4/2 NM-B (unlikely it seems), SE/SEU 4-4-6 copper, SE/SEU 2-2-6 AL, or go with #4 x 2 and #6 x 1 (ground) THHN in conduit across the attic, and down through the wall.
I looked briefly and haven't seen 4/2 NM-B. I really don't feel like running that much conduit for THHN and I'd like to save as much space in the conduit as possible, so aluminum is out. That pretty much leaves me with SE/SEU 4-4-6 which seems hard to find.
Am I missing anything obvious? Thx,
The boiler is an electric unit rated at 12KW (240V). The literature lists a maximum 50A draw. They specify a 70 amp double-pole breaker and 4 gauge copper wire.
My problem/question is with the 4 gauge wire and what options I have. I have 2" conduit running out the top of my service panel into the attic over the shop. The wire will exit the conduit, cross the attic, then drop down through an interior wall into the closet/bathroom where the radiant heat panel will be mounted. The total run going up, across and down will be approximately 50ft.
As best I can tell my options are finding 4/2 NM-B (unlikely it seems), SE/SEU 4-4-6 copper, SE/SEU 2-2-6 AL, or go with #4 x 2 and #6 x 1 (ground) THHN in conduit across the attic, and down through the wall.
I looked briefly and haven't seen 4/2 NM-B. I really don't feel like running that much conduit for THHN and I'd like to save as much space in the conduit as possible, so aluminum is out. That pretty much leaves me with SE/SEU 4-4-6 which seems hard to find.
Am I missing anything obvious? Thx,