shooon
Well-known member
When it get's really cold outside (-15 to -20 F) my system isn't flowing enough to fire the in floor heat. If I rig up a bypass loop between supply and return manifold the heater fires up, I can close the loop and it continues to run fine.
The heater has a 0.40 GPM activation flow with 0.26GPM min flow to maintain. I'm thinking the glycol is getting too thick to flow enough to meet the activation permissive. Everything works fine when its not brutally cold. Used a refractometer and I'm rocking a 52/48 propyelene mix so I dont think ill want to dilute anymore. 4 loop manifold with 200 - 220' loops of 1/2" pex pushed by a grundfos 15-58 on highest speed setting.
I have a probe in the slab right now and am trying to maintain the slab at 40 F until I get the ceiling fully insulated. I might just keep the slab at around 40 to 45 F and use my reznor heater when I want to work in there.
Just wondering how to address this issue. Had a couple ideas was wondering if someone had any better suggestions?
-Second pump in parallel or 1555 pump to boost gpm ?
-reverse acting thermostat loop between supply and return manifold: closes bypass when hot coolant (90 - 100 F) flows across it ?
-Zone control valve plumbed in as bypass loop on time delay timer: kicks off after 30 seconds of pump receiving power ?
The heater has a 0.40 GPM activation flow with 0.26GPM min flow to maintain. I'm thinking the glycol is getting too thick to flow enough to meet the activation permissive. Everything works fine when its not brutally cold. Used a refractometer and I'm rocking a 52/48 propyelene mix so I dont think ill want to dilute anymore. 4 loop manifold with 200 - 220' loops of 1/2" pex pushed by a grundfos 15-58 on highest speed setting.
I have a probe in the slab right now and am trying to maintain the slab at 40 F until I get the ceiling fully insulated. I might just keep the slab at around 40 to 45 F and use my reznor heater when I want to work in there.
Just wondering how to address this issue. Had a couple ideas was wondering if someone had any better suggestions?
-Second pump in parallel or 1555 pump to boost gpm ?
-reverse acting thermostat loop between supply and return manifold: closes bypass when hot coolant (90 - 100 F) flows across it ?
-Zone control valve plumbed in as bypass loop on time delay timer: kicks off after 30 seconds of pump receiving power ?