Hello everybody,

First I want to say thank you to this whole community. I was able to learn a lot to help me in building process of my workshop.
I have a shop area approximately 1400 ft.² that I'm looking to heat with radiant heat. I have built a 5 inch slab which is thermally separated from outside with a two inch Styrofoam insulation from the sides and the bottom. I have ran approximately 2000 feet of half-inch PEX. I have eight runs approximately between 250 in 300 feet long.
I am looking for some help to tie everything together. I drew a little sketch up of what I learned here at the forum how my system should possibly look on the wall, does that portion look okay?
I have also installed half-inch PEX going from my utility room to the middle of the slab, approximately 12 feet, so i'm planing to slide in a little concrete sensor.
So this is the part that I'm not quite sure.
I'm assuming the pump is going to be 110 and the thermostat is low-voltage, how do I tie in thermostat pump and a sensor together, what kind of a controller box or anything do I need? Size of my pump?

This is one zone only.

Help is greatly appreciated :)

Darko





100 (1)_resize.jpg

100 (2)_resize.JPG

radiant.jpg
 
To avoid these ads, REGISTER NOW!
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
Forgot to mention that I'm going with instant hot water heater.
I called eco-smart and talk to their tech guy, he recommended eco-smart 18 for my size of the shop.
Since this is going to be a close loop, what kind of antifreeze should I use?

Thanks
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,988
Location
West central Indiana
Are the fill valves actually purge valves? If not they will not work like that, at least not without an additional valve. I would put pressure Gage's where the fill valves are to see pump pressure/differential.

Your local electric company is going to have quite a bonus in the future!
 
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
Thanks for your quick reply!

I was thinking a lot about should I do this with electric or not, I do have a gas available at my house but I have decided to go with the electric because I'm going to install solar panels on my roof in a year or two, price of solar panels has come down a LOT in the last couple years so hopefully my electrical company is going to love me for a first year or two :). Forgot to mention that my walls are two by six with a spray foam insulation so that should help.

I have updated my drawing, hopefully things look a little bit clearer now.

Firebrick43
I have now filled/purge valve in front of the pump, is that okay?

I have removed the pressure gauges by the electrical heater because the stainless steel manifold comes preinstalled with pressure and temperature gauges so I guess I shouldn't need those.

So this is what I'm not still clear on:

1.What thermostat should I use, this is going to be heat only?

2.What slab sensor should I use? When I was pouring the concrete i installed the piece of half-inch PEX pipe that goes to the middle of the slab so I can insert the sensor later.

3.Does the slab sensor connects to a thermostat or a taco switching relay?

Thanks for your helpradiant2.jpg
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,988
Location
West central Indiana
You need two bib/drain to purge air. It just needs a valve between them so purge fluid doesn't take the short route but the long way around. A purge valve has a valve and bib/drain in one.

I would consider an outdoor reset instead of slab temp control. Slab temp is very slow to respond to load changes.
 
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
Sorry if I seem slow but a lot of this stuff is new to me.

I am looking at Paxuniverse.com http://www.pexuniverse.com/webstone-pro-pal-48613-purge-and-fill-valve48613-01.jpg
is that what you're describing "3/4" NPT Threaded Purge & Fill Ball Valve w/ Hose Drains"
it comes with a valve between them.

Can you tell me more about the "outdoor reset", I was under impression that having a slab sensor is a little bit better then just having thermostat on the wall by itself but I wasn't aware of the "outdoor reset" that your mentioning
 
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
I know you won't want to hear this, but I would go with a natural gas fired boiler designed to be used with this type of heating system.
I'm going to be using a lot of electricity there, different woodworking machines and a lots of welding.
I'm pretty lucky that my roofline is facing south and I'll be able to fill the whole's outside with solar panels. On the long run this is going to save me a TON of money. I'm actually hoping that in the next 5 to 7 years storage battery prices are going to be cheap enough to be able to completely disconnect from the electrical company.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,988
Location
West central Indiana
Outdoor reset means the controller reads the outside temp, and some read the air and slab temp as well. It sees the outside falling in temp and it raises the temp of the floor before the floor even sees a drop due to the increased load. If the controller is set right it makes for a more even system.

You do realize the power and storage would cost north of of 60k if the price comes down significantly. The only way solar PV can come anywhere close is if it is driving a heat pump. Probably a geothermal.
 

kuhner

Active member
Joined
May 2, 2007
Messages
42
Location
South Eastern Ohio
Don't let the non-electric boiler folks scare you off.
I have a 32 x 40 block garage, 4" of foam on the outside, good doors, and in central Ohio. I went with an electric boiler because I didn't want an open flame in a garage that may have flammable vapors, gasoline, paint thinner stuff like that. I am on AEP and not the cheapest rates, minimum monthly bill just for service is 45/month. Over the last 5-6 years my average bill is about 100. Average, those big 150/month winter bills hurt, but average it out its not too bad. I use a Seicor boiler.
I keep the temp at 60 and have a small water heater, and usually spend a couple hours a day after my real job up there.
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
kuhner.....what is your kW/h cost ? Going to do an electric boiler.Thanks. Now back to our regularly scheduled program.....
 
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
The price of the electricity here in North Carolina is around 0.9 c kw

I have a six-inch of spray foam insulation and 2 inch of Styrofoam under the slab so i'm hoping it's not going to be too bad.


I have updated my final layout drawing, I would appreciate any inputradiant3.jpg

These are all the parts I am using

ECO 18 | 18kW Electric Tankless Water Heater
http://www.ecosmartus.com/products/radiant-floor-heater/eco-18/#product-tab2
3/4" Sweat, Spirovent Jr Air Eliminator
http://www.pexuniverse.com/spirotherm-vjs075-spirovent-3-4-air-eliminator
Extrol #15 Expansion Tank (2.0 Gal Volume)
http://www.pexuniverse.com/amtrol-extrol-15-expansion-tank
UPS15-58FC 3-Speed Circulator Pump w/ IFC, 1/25 HP, 115V
http://www.pexuniverse.com/grundfos-ups15-58fc-circulator-pump-59896341
3/4" NPT Threaded Purge & Fill Ball Valve w/ Hose Drains
http://www.pexuniverse.com/webstone-pro-pal-48613-purge-and-fill-valve
3/4" Pressure Relief Valve 30 psi (Lead-Free)
http://www.pexuniverse.com/wilkins-p1000axl-30c
3/4" Threaded Y-Strainer, Cast Bronze, with Plug (Lead-Free)
http://www.pexuniverse.com/3-4-threaded-y-strainer-cast-bronze-with-plug-lead-free-bronze
60 Amp 240-Volt Non-Fuse Metallic AC Disconnect
http://www.homedepot.com/p/GE-60-Amp-240-Volt-Non-Fuse-Metallic-AC-Disconnect-TFN60RCP/100674085
8-branch Stainless Steel Radiant Heat Manifold Set w/ 1/2" PEX adapters
http://www.pexuniverse.com/ssm108-steel-radiant-heat-manifold
Taco SR501 Single zone switching relay
http://www.pexuniverse.com/taco-sr501-4-switching-relay
tekmarNet® Thermostat 552 - One Stage Heat
http://tekmarcontrols.com/products/zoning/552.html
Outdoor Sensor 070
http://tekmarcontrols.com/products/accessories/070.html
Slab Sensor 079 - 10' (3 m) wire
http://tekmarcontrols.com/products/accessories/079.html
 

coldh2o

Well-known member
Joined
May 21, 2013
Messages
1,414
Location
Ontario, Canada
You don't need that purge & fill valve, there are valves for that purpose on the manifold.

I would put a hose bib/boiler drain at the lowest part of your system so you can drain the piping if need be.

Ball valves either side of the pump so it can be removed without draining the system.
 
To avoid these ads, REGISTER NOW!
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
coldh2o,

Thanks for your input, you are absolutely right purge and fill valves are on the manifold I don't know how I missed that.


I have updated my drawing with your suggestionsradiant4.jpg
 

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
Don't let the non-electric boiler folks scare you off.
I have a 32 x 40 block garage, 4" of foam on the outside, good doors, and in central Ohio. I went with an electric boiler because I didn't want an open flame in a garage that may have flammable vapors, gasoline, paint thinner stuff like that. I am on AEP and not the cheapest rates, minimum monthly bill just for service is 45/month. Over the last 5-6 years my average bill is about 100. Average, those big 150/month winter bills hurt, but average it out its not too bad. I use a Seicor boiler.
I keep the temp at 60 and have a small water heater, and usually spend a couple hours a day after my real job up there.

kuhner.....what is your kW/h cost ? Going to do an electric boiler.Thanks. Now back to our regularly scheduled program.....


I'm in the same frame of mind, safety, convenience, price, and existing equip has forced my hand to using electric. My 30x40 shop's average monthly bill for the past 12 months has been $65. 8 months really low, 4 months of high bills each year. The electric is dead quiet, safe and reliable.
I've run the same electric on-demand heater for 7 years with not one single issue.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Nobody ever said that electric doesn't work, just the opposite, it works and works very well. It's just that the cost to use it is quite a bit more than using some of the other energy sources.
 
Last edited:
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
Things guys for the info,

those electrical charges seems pretty reasonable, I love working with lacquer and having sawdust, lacquer and open flame in the same building terrifies me.

10 years ago my wife and I took a vacation to Banff Canada and this was the first time I experienced radiant heat, and I decided then that this is the only heat I will ever do in my house or workshop.

Any other input, or anything else I'm missing in my design?radiant4.jpg
 

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
The price of the electricity here in North Carolina is around 0.9 c kw
There's no place in the US with power under a penny per kWh. Your rate is probably 9 cents/kWh, not 0.9 cents.

I mention because a factor of 10 matters if you're basing "Ah, that won't be too bad" on a cost that's 1/10th of real.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,077
Location
SE MI
Nobody ever said that electric doesn't work, just the opposite, it works and works very well. It's just that the cost to use it is quite a bit more than using some of the other energy sources.

More like EVERY OTHER heat source !

Lots of insulation will help. Adding any amount of solar that can be sold back is a big win. This varies by location.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,077
Location
SE MI
10 years ago my wife and I took a vacation to Banff Canada and this was the first time I experienced radiant heat, and I decided then that this is the only heat I will ever do in my house or workshop.
I can't argue with that !

If you don't mind, what do you estimate the cost of the all the plumbing and boiler to be ?

A friend of a friend was quoted >$40k on a new build of about 3200 sq ft. (Walk out basement and ground floor.) Seems very high to me.
 
OP
D

Darko9000

Member
Joined
Jan 31, 2014
Messages
13
Location
NC USA
If I remember correctly 2000 feet of PEX tubing was about $500, the other miscellaneous little things like zip ties was another hundred bucks.
My friend let me use his copper manifolds to pressurize the system during concrete pouring
if you look in one of the earlier posts I have the list of all the things I'm going to order

ECO 18 | 18kW Electric Tankless Water Heater is around $360 on Amazon

Pretty much everything else is from pexuniverse around $750

If you include another $200 for 2-40 amp breakers and miscellaneous copper fittings


The total material price is roughly $2000

I used one of the free software for a month to do the piping layout, I cannot remember the name of it now. A friend of mine helped me lay down all the pipe and strap everything

This is a building 25 x 60 12 feet tall excluding utility room I am heating roughly 1400 ft.²,

Couple years ago we had one of those homes shows with a lots of businesses advertising their services so I called one of the companies and the price was over $10,000 I cannot remember what it was exactly.

2015-04-01 17-05-07_resize.JPG

2015-05-06 17-06-34_resize.JPG

2015-05-06 17-10-59_resize.JPG

2015-05-07 08-24-52_resize.JPG

2015-06-14 14-05-11_resize.JPG

2016-07-26 08-35-08_resize.JPG

2016-09-09 13-09-19_resize.JPG
 

mustangfan

Well-known member
Joined
Jul 3, 2011
Messages
49
Some people do not like Radiant heat for some reason or another. I am not sure if their system was designed correctly or what. I like the fact it can be -20 outside and if I want to walk around barefoot on the concrete, I can. In my workshop with hot air, you won't be waking around without shoes on because the concrete is always COLD>

In our house, we put the tubes under the floor in our kitchen. Our kitchen and Dining room both have crawl space under them. We do not have the radiant/in floor in the Dining room yet.
Last winter the temp in the kitchen at 6 feet up was 68', the temp in the dining room at 6 feet up was 66'.
BUT the floor temp of the kitchen was 75 and the floor temp of the dining room was 55'
Big difference when you heat the floor!!
Your setup looks good. You will also be able to get some FREE radiant from the windows!!
ENJOY
 