Radiant Hydronic Tuning Tips...?

86turbodsl

Well-known member
Joined
Jul 1, 2005
Messages
6,554
Location
Michigan
Keep in mind big delta T's on supply/return also means more variation in floor surface temps. I don't like big delta's in my designs. I shoot for about 20F maybe 25 at the top.
 
To avoid these ads, REGISTER NOW!

UpstateNY

Well-known member
Joined
Jan 2, 2012
Messages
662
Keep in mind big delta T's on supply/return also means more variation in floor surface temps. I don't like big delta's in my designs. I shoot for about 20F maybe 25 at the top.

Yea, mine works on a 20F delta. Also, I have the T-stat with both a slab temp sensor and air temp sensor. Since I installed a slab probe into my slab I use that as it's the preferred method. My Tstat displays both readings. TDKart is correct, your slab temp will typically be about 2-3 degrees higher than the air temp.

I also have a switch inside my house so I can turn on the shop radiant from there as well. I pre-heat the shop before I go out there. I also have a wireless temp gauge in the house so I can read the shop air temp and humidity so I know if something has gone whacky.
 
Last edited:
OP
H

Holeshot

Active member
Joined
Aug 6, 2007
Messages
30
Location
Eaton County, MI
What does everyone like for t-stats (preferably 802.11x WiFi enabled)?

For the sake of simplicity, I'd love to use a line voltage t-stat...but having the ability to control and track runtime is needed.

What is a typical return temp when the slab surface is say 65°F?

Thanks again, gents!

Beers,

Matt
 
To avoid these ads, REGISTER NOW!

kabinenroller

Well-known member
Joined
Sep 14, 2013
Messages
897
Location
S.E. Wisconsin USA
I also have a wireless thermometer in the house that monitors the temp. in the shop. 145' from sensor in the shop to the house unit. It works just fine even with metallic window shade down on the only window on the front fascia of the building.
 

Modoc

Well-known member
Joined
Jan 25, 2014
Messages
167
Location
SE Oregon
Sure miss anthony666, great debate and facts gentlemen... I think this has been one of the more useful and pertinent threads regarding hydronic operation!

Boo Yaa!
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
Jackfre,


In this equation: At 2.3 gpm x say a 20* delta T x500 =23,000 btu input. Where does the 500 value come from ?

The 500 is a constant base upon the specific heat of water. That value would change if you have glycol in the system.
 