Well-known member
I have a Weil Mclain hot water oil boiler. It is set-up right now with a 4 zone baseboard system. The upper limit is set at 200*F and the lower limit set at 180*F.
I recently added a radiant system to the addition of the house. I have 4 loops (3) 225' and (1) 245' (slight miscalculation on my part!)
The issue I am having is getting the supply temp down to 120-125*F. I have utilized a tempering valve. The problem is the heat loss through the loops is so minimal, I cannot get the return water "cold" enough to mix with the supply water to get the desired supply temp.
I installed the pex 8" on center staple up under the plywood subfloor. Installed a reflective radiant barrier, and then closed cell spray foam insulation.
I have heard of utilizing a "cold loop" to the supply, but I don't see how that will work. I have a closed system, and would prefer to keep it that way!
Any help would be greatly appreciated.
Thanks, Tim