So, since I'm not having any luck finding an HVAC contractor available/willing to look at finishing the radiant system for my shop, I decided to attempt the design myself.
I performed a ACCA Manual J calculation using the calculator on builditsolar.com and I know the free stuff online should only be used as a rough guide but the calculated heat load seemed extremely low for a 3000 sqft building. The calculator came out with 51,450 btu/hr design loss. So, to the heating experts on here, does this seem too low or am I on the right track?
Below are the specs/assumptions:
-0*F design temperature
-5500 degree days (used Harrisburg, PA as closest reference)
-50'x60'x14' pole building, steel panel walls inside and out, no housewrap
-R38 blown cellulose in 3000 sqft of ceiling
-Approximately 7" of blown cellulose in all walls assumed R21
-12'x16' R13 overhead door and standard 3' (R3 assumed) man door on North wall
-8'x8' R13 overhead door on East wall
-Standard 3' (R3 assumed) man door on South wall
-8'x8' R13 overhead door on West wall
-220' perimeter assumed to have effective R-value of 2 (has 2" R10 foamboard under entire slab and around perimeter except overhead door openings)
-42000 cuft total building volume assumed to have 0.5 air change/hr infiltration (design loss increased to 77,900 btu/hr with 1 air change/hr infiltration value)
I performed a ACCA Manual J calculation using the calculator on builditsolar.com and I know the free stuff online should only be used as a rough guide but the calculated heat load seemed extremely low for a 3000 sqft building. The calculator came out with 51,450 btu/hr design loss. So, to the heating experts on here, does this seem too low or am I on the right track?
Below are the specs/assumptions:
-0*F design temperature
-5500 degree days (used Harrisburg, PA as closest reference)
-50'x60'x14' pole building, steel panel walls inside and out, no housewrap
-R38 blown cellulose in 3000 sqft of ceiling
-Approximately 7" of blown cellulose in all walls assumed R21
-12'x16' R13 overhead door and standard 3' (R3 assumed) man door on North wall
-8'x8' R13 overhead door on East wall
-Standard 3' (R3 assumed) man door on South wall
-8'x8' R13 overhead door on West wall
-220' perimeter assumed to have effective R-value of 2 (has 2" R10 foamboard under entire slab and around perimeter except overhead door openings)
-42000 cuft total building volume assumed to have 0.5 air change/hr infiltration (design loss increased to 77,900 btu/hr with 1 air change/hr infiltration value)