Im heating my building with a propane fired commercial hot water tank and Im in the middle of plumbing. My pump is on the return side and I was planning on putting the tank where the piping leaves off in the pic..But Im reading its supposed to go on the suction side of the pump.. Anyone have any suggestions on what I should do? Should I remove the vertical run where the pump is and turn it horizontal and put the tank behind the pump? See pic. Thanks!
 

Attachments

  • IMG_5102.jpg
    IMG_5102.jpg
    139.3 KB · Views: 61
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I do all my radiant set-up flooring the book ... "pumping away".

Did you do a heat load? -- what's the BTU of the WH?
 
OP
T

tmcelheny

Member
Joined
Dec 23, 2014
Messages
22
Location
PA
I do all my radiant set-up flooring the book ... "pumping away".

Did you do a heat load? -- what's the BTU of the WH?

I had a heat loss done. They calculated 42k BTU unit was required. The unit is a 50k BTU. I have spoken with an engineer this morning and realize I will need to relocate the pump to be ahead of the expansion tank so its on the suction side. So the plan will be to put the pump up near where the tank was going to be and the tank behind.

Have been advised the pump could be on supply or return, just so the pump didn't have to overcome the pressure from the expansion tank prior to system.
 
Last edited:
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I normally exit the boiler and go to a spirovent -- use the tap under for the expansion tank and have the boiler make up water come in between the two with a tee.

The pump is next -- so it pumps away from spirovent and into manifold.

With a true boiler you need a primary secondary -- or constant circulation to the highest temp manifold loop.

Return manifold back to boiler.


Feed to the boiler is back flow preventer and feed valve
 

86turbodsl

Well-known member
Joined
Jul 1, 2005
Messages
6,554
Location
Michigan
yeldogt is right, you want the inlet of the pump to be upstream of the spirovent so the reduced pressure on the inlet drops the pressure and bubbles can be vented in the vent. Also the increased pressure AFTER the pump can enhance heat transfer into your load.

(edit) that sounds wonky, but the point is there... lol...
 