Newbe here! Really impressed with the posts on this site. Seems like someone always knows what to do. I am planning a 50 by 50 building for next spring construction. I am using radiant floor heat but am having a hard time coming up with a tubing schematic and the number of zones needed. Anyone have any ideas?
 
To avoid these ads, REGISTER NOW!

mybuickgs

Well-known member
Joined
Sep 8, 2009
Messages
58
Location
Kansas
use the search function on the forum. You will have a good week of reading if you follow all the threads.
 
To avoid these ads, REGISTER NOW!

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
First, please fill in something for a location in your profile. Especially for heating and cooling questions it helps us to know if you're in Canada or Texas.

Do a search in this forum for "radiant" you will find tons of info, including links to some very good radiant heating suppliers.

Quickly, 50x50 is 2500 sq/ft. general rule of thumb says 1ft of tubing per sq/ft, so 2500 ft of tubing, with an approx. maximum loop length of 300ft. This means you will need 8 loops minimum.
If you plan on keeping an open building with no interior walls you can do it all in one zone, if you are thinking dividing the interior you will want to look at seperating the system with zone controls.
 