Hi all, Part of my house is a slab with radiant tubing. The other half is basement with floor trusses for upstairs. I want to run staple up tubing between the trusses for upstairs. With all the plumbing and electrical there isn't room to run long runs of tubing at a time. If I did each truss, 65 ft. of tube, I would need to put a splice to join to the next truss. Would that be ok? I'd need 4 splices per zone. Is that just asking for trouble? or no big deal?...Thanks
 
To avoid these ads, REGISTER NOW!

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
If they will be accessible go for it , joints are never desirable but some times necessary.
Just mark where they are on the joist or a PC of paper for future reference.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Do some research on the staple up -- you will not get a lot of BTU's out of that type of system.

A proper load calculation needs to be done. I used AL pipe and extruded heat plates ... and I still had to run hotter water than I anticipated. I installed a supplemental Runtal unit in one room.
 
To avoid these ads, REGISTER NOW!

36truck

Well-known member
Joined
Jul 13, 2010
Messages
980
Location
UP of Michigan
I did my upper floor using light weight gypecrete. Poured 1" thick over the pex pipes. Works great give you a good heat sink. Staple up has a very low BTU through the floor plus over heating the sub floor.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
Do some research on the staple up -- you will not get a lot of BTU's out of that type of system.

A proper load calculation needs to be done. I used AL pipe and extruded heat plates ... and I still had to run hotter water than I anticipated. I installed a supplemental Runtal unit in one room.


Load calculation in radiant heating mostly apply for the boiler size , the standard spacing for all staple up is 8" centers , unless there are some very unusual situations.
Never go less than the industry standard of 8" centers for staple up., I have been on many jobs where they thought they could get away with less. And having to do it all over.

What water temp did you think you needed . I have staple up , insulated floor joist and I'm running low temps. You need to insulated the joist cavity or it won't work as intended.

You don't give enough info to determine what's wrong.
 
Last edited:

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
When designing radiant floor heating systems we start with a room-by-room Manual J heat load analysis. This is the only way to determine what, if any, radiant floor system will work.

It is particularly crucial to run accurate heat loads when using sub-floor or sandwich applications. Unless you are living below the Mason/Dixon a true "staple-up" is unwise, requiring higher water temperatures often coming up short of the required output.

Here in Minneapolis, and designs for others in cold climates, we use extruded aluminum plates almost exclusively and haven't used a bare tube, stapled to or suspended from, the sub-floor since 1991.

As far as couplings go, it is expensive and less than ideal. Thread the pipe where you can and use 3/8" PEX if you know how.
 