Raising my garage ceiling height, a work in progress

Bob911

Member
Joined
Jun 1, 2010
Messages
7
Location
OH
My 20 x 24 garage has been adequate but never really satisfied my need/desire for a nice working garage, "working" as it relates to maintaining motorcycles, cars and other related projects. I'm not a professional by any means, this is just hobby stuff. I've lurked around the forum for a few years while I tried to figure out what to do differently (add a few feet in wall height, re-truss the roof and add height and an attic, knock it down and start over, etc.), with the primary goal of adding a 4 post storage/maintenance lift. Like anything else the cost/value ratio played a role and has kept me from doing a total rebuild, but I've been inspired by several posters here who vaulted their garage ceiling and have decided to proceed in that direction.
 
Last edited:
To avoid these ads, REGISTER NOW!

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
How are you carrying the load that will transfer down across the garage door? Did you beef up that header?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,106
Location
SE MI
Remind me to NEVER enter your garage after a heavy snow !

So one half of the weight of the entire roof (and snow load) is supported by a 2x8 face nailed to 2 2x4 studs ?

attachment.php


The other half of the weight of the entire roof (and snow load) is supported by a 2x8 supported on the garage door header ?

attachment.php


The primary purpose of those ceiling joist was to prevent the walls from bowing out. In theory, your new ridge beam SHOULD pick up the load and there would be very little horizontal force where the rafter connects to the wall.

Just "for fun", at the center of the garage measure the distance between the 2 footers. Then, at the same location, measure the distance between the top plates.

Wait until spring and you have had a few good snows. Check your measurements again. If the top plates are more than about 1/2" do yourself a favor. Temporarily put a 4x4 post in the center and apply some force on your new ridge beam. Get a come-a-long, connect it to the top plate at each rafter and pull the wall in until in matches the distance at the floor. Now, add a collar tie between the 2 rafter just below the new ridge beam.

You need to run a 4x6 post from the ridge beam at the back wall from that face nailed 2x8 down to the floor. Rest it on a block 4x6 block of PT. At the front, you said you wanted to change the header. You are going to need to go steel to span the garage door and at each end of the steel box/I-beam you need some more 4x6 posts.
 

Attachments

  • Capture1.JPG
    Capture1.JPG
    56.6 KB · Views: 215
  • Capture2.JPG
    Capture2.JPG
    66.8 KB · Views: 211
Last edited:

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
Remind me to NEVER enter your garage after a heavy snow !



So one half of the weight of the entire roof (and snow load) is supported by a 2x8 face nailed to 2 2x4 studs ?



attachment.php




The other half of the weight of the entire roof (and snow load) is supported by a 2x8 supported on the garage door header ?



attachment.php




Just "for fun", at the center of the garage measure the distance between the 2 footers. Then, at the same location, measure the distance between the headers.



Lol let’s hope he isn’t done. But looking how it is I’m gonna guess he has no plan tearing out the door and putting in a beam which might support the roof load. Not sure what size that would require.

In my mind neither side is aloud to be loaded because there’s most likely no post under the other side and no footing there other than what the garage originally had. It would require a larger pad to support half the roof load.

Do you have a building permit and proper drawings? Or just winging it?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,106
Location
SE MI
Of yeah. I forgot to mention. If there is a structural failure while you are living there, your insurance company likely will not cover it because the structure was changed without any approved engineering drawings. When you go to sell the house, most states would require that you tell the buyer that there were non-approved structural changes made to the building. That will really help the value !
 
To avoid these ads, REGISTER NOW!

PugetDude

ALLIANCE MEMBER
Joined
Mar 13, 2013
Messages
22,328
Location
Superstition Mountains, AZ
Remind me to NEVER enter your garage after a heavy snow !

So one half of the weight of the entire roof (and snow load) is supported by a 2x8 face nailed to 2 2x4 studs ?

attachment.php


The other half of the weight of the entire roof (and snow load) is supported by a 2x8 supported on the garage door header ?

attachment.php


The primary purpose of those ceiling joist was to prevent the walls from bowing out. In theory, your new ridge beam SHOULD pick up the load and there would be very little horizontal force where the rafter connects to the wall.

Just "for fun", at the center of the garage measure the distance between the 2 footers. Then, at the same location, measure the distance between the top plates.

Wait until spring and you have had a few good snows. Check your measurements again. If the top plates are more than about 1/2" do yourself a favor. Temporarily put a 4x4 post in the center and apply some force on your new ridge beam. Get a come-a-long, connect it to the top plate at each rafter and pull the wall in until in matches the distance at the floor. Now, add a collar tie between the 2 rafter just below the new ridge beam.

You need to run a 4x6 post from the ridge beam at the back wall from that face nailed 2x8 down to the floor. Rest it on a block 4x6 block of PT. At the front, you said you wanted to change the header. You are going to need to go steel to span the garage door and at each end of the steel box/I-beam you need some more 4x6 posts.

Count the nails in the 2x8... (hint: you can count them on one hand, even if you've suffered a horrific table saw accident..)
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,106
Location
SE MI
Lol let’s hope he isn’t done. But looking how it is I’m gonna guess he has no plan tearing out the door and putting in a beam which might support the roof load. Not sure what size that would require.
Steel !

Do you have a building permit and proper drawings? Or just winging it?
Permit would require engineering approved/stamped drawings !
 

spudley

Well-known member
Joined
Dec 27, 2016
Messages
702
Location
Northeast Wisconsin
How are you carrying the load that will transfer down across the garage door? Did you beef up that header?
From the posted pix, I see no evidence of any header upgrade. Looks like adequate sized lvls, with inadequate path to transfer the new load now that the rafter ties are removed. Hopefully there's some other support not visible.
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
From the posted pix, I see no evidence of any header upgrade. Looks like adequate sized lvls, with inadequate path to transfer the new load now that the rafter ties are removed. Hopefully there's some other support not visible.



Me thinks the header should have been swapped in prior to cutting the roof esp in winter.

The walls don’t look they were opened up either.
 