Ran into a Snag Planning My Lean-To Build

jrmyga23

Member
Joined
Aug 31, 2011
Messages
5
I have a 30x40 pole barn I want to add a lean-to onto. The plan is to cut away the steel panels just enough to expose the header. The problem is I have no purlins to attach the remaining steel paneling or the flashing I plan to trim it out with.
 

Attachments

  • image1.jpeg
    image1.jpeg
    394.3 KB · Views: 50
  • image0.jpeg
    image0.jpeg
    575.1 KB · Views: 50
To avoid these ads, REGISTER NOW!

vrstcv

Active member
Joined
Dec 3, 2020
Messages
31
Location
ne
You will have to add purlins as needed to catch your blue cut lines.
cut the tin then slip the new purlins in'
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,971
Location
Thousand Islands NYS
If you're using the existing header that supports the trusses, be sure it can support half the lean-to roof load. Don't know where you are. Around here it's a lot - 60psf.
 
To avoid these ads, REGISTER NOW!
OP
J

jrmyga23

Member
Joined
Aug 31, 2011
Messages
5
Roof load from where I live is 20 or 30psf. I have thought I could slip a Perlin in below the header once I have cut the steel paneling out of the way. Above the header the trusses extends out flush with the header. Is it possible to slip a Perlin between the trusses and toe nail it in or find a joist hanger that might work for this situation because truss plates will be in the way as well. Seems like I would need to attached this new Perlin that is going above the header to the header board itself.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,681
Location
Kingsport, TN
Have you considered exposing just part of the header? Much easier. I have to imagine you aren’t trying to hang 2 by 12 rafters
 