Ready for inspection, is this subpanel okay?

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
I put this subpanel into my barn and just landed the last circuit last night. The feed is only 60 amps and the fat circuit on the left is for a welder plug directly below the panel. Any obvious errors?
 

Attachments

  • IMAG0743.jpg
    IMAG0743.jpg
    93.8 KB · Views: 598
To avoid these ads, REGISTER NOW!

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
Looks clean. (not a code guy or pro).

Are the wires going into the box supposed to have clamps on them? (you have what looks like bushings, not clamps. Every box I've seen has clamps).

Are the wires going up out of the box stapled within 6" (or is it 8"?) The ones going down look like they are, not ones going up do not (but picture is cut off).

One item that helps in the future is to use a small bit of NM sheath to write the circuit name on it, then put it over the hot wire going into the breaker. Helps in the future so you know what is what with the panel off.
 
Last edited:
OP
H

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
No, the wires are not stapled within 6" but there are romex clamps in the panel knockouts. They are the plastic kind.

With these clamps and in this wall, must I staple the romex? how close to the panel?

From the panel I go through some blocking within three feet and then the top plate and then stapled to a block on top of the joist in the ceiling.

Thank you for the input, hope someone comes along that knows the requirement for this.
 
Last edited:

dbonne

Well-known member
Joined
Apr 18, 2013
Messages
305
Location
Southern Idaho
NEC 334.30 (for NM cable) states that cable shall be supported within 12 inches of every outlet box, junction box, cabinet, or fitting.
 

dbonne

Well-known member
Joined
Apr 18, 2013
Messages
305
Location
Southern Idaho
One other thing, Highbeam, Depending on your inspector and jurisdiction, you may need to reidentify that white wire (the one you have a wrap of black tape on) entirely to the conduit fitting where it enters the box.

Panel looks sweet! Nice work.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I would have installed that panel with the main breaker on the bottom.

*And please no one use the word upside-down.
 
To avoid these ads, REGISTER NOW!

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,868
I may be missing it but I don't see the main neutral wire coming in from the top like the power and ground wires do. Neat work if you have it hidden with the other neutrals but you should make it plain that it comes in with the other main lines.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Only a 60 amp feeder on 6 gauge THWN between main and sub, then a 100 amp main breaker (disconnect) in the sub. I have LOTS of convenience outlets.

6 AWG is rated for 37 amps for power transmission. I expect the inspector will fail it for that, a 60 amp circuit needs 4 AWG.
 
OP
H

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
6 AWG is rated for 37 amps for power transmission. I expect the inspector will fail it for that, a 60 amp circuit needs 4 AWG.

The subpanel passed a year ago but with only a few circuits. It is a 4 wire feed from the main panel in the house. 60 amp breaker at the main panel. Same as the 60 amp breaker that feeds my hot tub with 6 gauge.

Not sure about the "power transmission" difference but the regular chart says 6 guage NM is good for 55 but you can round up to 60 so that's what I did and the inspector allowed it.

The white wire is there but is hard to see since it is so small. The more circuits I add, the smaller that the 6 gauge looks!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
6 AWG is rated for 37 amps for power transmission. I expect the inspector will fail it for that, a 60 amp circuit needs 4 AWG.

HuH? #6 THWN is rated for 65a[NEC 2011 310.15(b)(6)] Where did u come up with 37a? :dunno: And service entrance conductors(what I think youre calling power transmission) are sized on a different table AND they have higher ampacity ratings than branch circuit ratings! But a feeder to a garage IS NOT a service entrance conductor!

The subpanel passed a year ago but with only a few circuits. It is a 4 wire feed from the main panel in the house. 60 amp breaker at the main panel. Same as the 60 amp breaker that feeds my hot tub with 6 gauge.

Not sure about the "power transmission" difference but the regular chart says 6 guage NM is good for 55 but you can round up to 60 so that's what I did and the inspector allowed it.

The white wire is there but is hard to see since it is so small. The more circuits I add, the smaller that the 6 gauge looks!

U didnt use Romex for your feeder, u used THWN so im not sure why u brought up Romex. Anyhow, yes, #6 Romex does have an ampacity of 55a(60c deg column). THWN has a 65a ampacity because it would be sized on the 75c deg column! So i wouldnt worry about the feeder!
 
Last edited:
OP
H

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Hu



U didnt use Romex for your feeder, u used THWN so im not sure why u brought up Romex. Anyhow, yes, #6 Romex does have an ampacity of 55a(60c deg column). THWN has a 65a ampacity because it would be sized on the 75c deg column! So i wouldnt worry about the feeder!

Well, yes, I did. What you can't see is that between the subpanel and the main panel I have a junction box at the house in the house garage where I used to have a welder plug fed by 6/3 romex. At that junction box I switched to conduit and thwn for the outside part of the run. So I treated the whole run as romex nm with the lower 60 amp limit. All inspected of course.
 
OP
H

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Here is another shot of what's going on above the panel. Based on the advice here I believe that I must install an additional block within 12" of the top of the panel and staple each romex cable to the block. Correct?
 

Attachments

  • IMAG0744.jpg
    IMAG0744.jpg
    65.2 KB · Views: 151

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Correct.

What is that green screw doing there. Have you installed that bonding screw making this service equipment? In other words, have you mistakenly bonded the equipment grounding buss to the neutral buss?
 

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
Correct.

What is that green screw doing there. Have you installed that bonding screw making this service equipment? In other words, have you mistakenly bonded the equipment grounding buss to the neutral buss?

It looks like that green screw is on the ground bar only, bonding the ground bar to the panel case. Should be ok as long as isn't on the neutral bar.
 
OP
H

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Correct.

What is that green screw doing there. Have you installed that bonding screw making this service equipment? In other words, have you mistakenly bonded the equipment grounding buss to the neutral buss?

On this siemens panel that green screw comes from the factory loosened and then you tighten it into the panel to bond the ground buss to the panel. The instructions even tell you to do that before mounting onto a wall so that you are able to get a good torque on it.

The neutral buss (on left) is insulated from the panel but comes from the factory with a thick brass bar that runs from one buss to the other. That bar was removed to provide the isolated neutral at the sub.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
Well, yes, I did. What you can't see is that between the subpanel and the main panel I have a junction box at the house in the house garage where I used to have a welder plug fed by 6/3 romex. At that junction box I switched to conduit and thwn for the outside part of the run. So I treated the whole run as romex nm with the lower 60 amp limit. All inspected of course.

O ok. Got it. Then u did it correctly!
 