After a couple years of living with only temporary power to my detached garage, I have lined up a guy with a Kubota BX25 to dig a trench 125' from my house to the detached garage so I can run a 100A service to the garage off the 200A main panel in my house. I told him I want the trench 30" deep. In the trench will be:
1 1/2" PVC schedule 40 conduit for electrical feed to garage
1 1/2" PVC schedule 40 conduit as sleeve for a 3/4 PEX seasonal water line
1" PVC schedule 40 conduit for communications cables
Caution tape
I have a 1 1/2" PVC conduit stubbed up through the slab and into a stud bay, so I'm kind of locked into that conduit size if I want to use my existing stub-up.
I am planning to run (3) #3 CU THHN/THWN conductors plus (1) #8 CU ground in the 1 1/2" PVC conduit. I also want to run (3) #12 wires backto the house as a 3-way switch leg for the light outside my service door. Do I run into any trouble with derating or fill if I put these in the same conduit with the feeders? Would it be better if I ran a separate conduit for the switch leg wires?
Trench length is 125'. Total wire length panel-to-panel will be 140'.
Now I'll probably get about a 100 posts about how AL is much cheaper than CU (I am hoping it will drop a little before I buy the wire!) and how I should run a 2" conduit for easier pulling, but other than that am I missing anyting? Any obvious code violations or potential problems? (On 2008 NEC, no applicable local amendments.)
1 1/2" PVC schedule 40 conduit for electrical feed to garage
1 1/2" PVC schedule 40 conduit as sleeve for a 3/4 PEX seasonal water line
1" PVC schedule 40 conduit for communications cables
Caution tape
I have a 1 1/2" PVC conduit stubbed up through the slab and into a stud bay, so I'm kind of locked into that conduit size if I want to use my existing stub-up.
I am planning to run (3) #3 CU THHN/THWN conductors plus (1) #8 CU ground in the 1 1/2" PVC conduit. I also want to run (3) #12 wires backto the house as a 3-way switch leg for the light outside my service door. Do I run into any trouble with derating or fill if I put these in the same conduit with the feeders? Would it be better if I ran a separate conduit for the switch leg wires?
Trench length is 125'. Total wire length panel-to-panel will be 140'.
Now I'll probably get about a 100 posts about how AL is much cheaper than CU (I am hoping it will drop a little before I buy the wire!) and how I should run a 2" conduit for easier pulling, but other than that am I missing anyting? Any obvious code violations or potential problems? (On 2008 NEC, no applicable local amendments.)