Really basic quesitons about wiring florescents in continuous row

snorky18

Well-known member
Joined
Oct 1, 2007
Messages
1,170
Location
Southeast Tennessee
I've done a lot of electrical work, but I've never wired florescent fixtures in a continuous row before.

I know that the fixtures have to be rated for continuous row wiring. Mine are.

Is the entire fixture basically considered a giant junction box / raceway?

What type of wire should I use between the fixtures? NM, or just plain THHN cable?

I'm assuming each fixture needs to be grounded individually?

Are the basic steps basically bring power into the first fixture through a KO, connect the ballast along with another set of wires to run down to the next fixture, and rinse, lather, repeat till you get to the end of the row?
 
To avoid these ads, REGISTER NOW!
OP
S

snorky18

Well-known member
Joined
Oct 1, 2007
Messages
1,170
Location
Southeast Tennessee
No one locally sells THHN by the foot, except for home depot who mark it up something ridiculous.

Can I use romex / NM inside the fixture instead?
 
To avoid these ads, REGISTER NOW!

ReefBlue

Member
Joined
Apr 14, 2005
Messages
9
Location
Delco, PA
Are the basic steps basically bring power into the first fixture through a KO, connect the ballast along with another set of wires to run down to the next fixture, and rinse, lather, repeat till you get to the end of the row?

That's it.

Each fixture does have to be grounded, but those grounds can be chained together also.

I use 12-2 MC for everything. This way I don't have to worry about adding more lights in the future and then overloading the beginning of the branch wiring. . .
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,751
That's it.

Each fixture does have to be grounded, but those grounds can be chained together also.

I use 12-2 MC for everything. This way I don't have to worry about adding more lights in the future and then overloading the beginning of the branch wiring. . .

If the fixtures are connected together, they are bonded together, & the grounding conductor does not need to connected at every one, as the fixture channel is the grounding conductor.
 