rebar spacing

mikewatson

Well-known member
Joined
Sep 18, 2013
Messages
56
Location
sheboygan wi
Im going to be pouring a 42 by 60 x4 in 5 bag mix floor, i see most people on here space rebar in 12" squares in there buildings . now my buddy say they place rebar in 5 ft squares but i dont see any one else doing this . he works for a big concrete company also . I was thinking of using mesh and rebar around where the lift would be ,but he say no just use rebar 5ft squares is all you need because if it cracks the rebar with hold it from shifting up . Iam in cental wi and will be doing infloor heat an 2in insulation under if that matters. im thinking this is incorrect doing 5ft sq's
 
Last edited:
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
I wouldn't do 5 ft squares in Maine, 1 foot squares may be overkill but it works and I'd rather do my slab one time only

Sent from my XT901 using Tapatalk
 

R-132 Fan

Well-known member
Joined
Feb 27, 2010
Messages
441
Location
Central Texas, East of Austin
I have seen 24" squares on a lot of commercial work. This was in tilt wall warehouses. Five foot spacing just seems way too far apart.
Better to build a little heavy then skimp and regret it later on.
 

May Pop

Well-known member
Joined
Aug 7, 2005
Messages
783
Location
Lake in the hills Il.
We did my sons in Milwaukee this summer. 24" and extra around the edges and the door openings. 29 x 28 with the apron and it cost about 300 bucks + delivery. Menards, No cracks yet I hope.
I felt it was worth the extra bucks over mesh.
 

LX-Markham

Well-known member
Joined
Apr 27, 2013
Messages
2,929
Location
Markham, Ont.
Also depends on what size of rebar.
12"-16" spacing is fairly typical.

5'-0" spacing? Maybe your buddy that works for the concrete company was talking about saw cuts?
 

Ray-CA

Well-known member
Joined
Jan 6, 2007
Messages
3,451
Location
San Diego CA
When they poured our 28x30 as well as the driveway, they put the re-bar 18-inches on center.

Ray
 

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,378
Location
Central Maine
Spacing rebar at 5' seems a bit wide but it may not be as crazy as it sounds. Reinforcing in a slab is based on the cross sectional area of the reinforcing relative to the slab section. I haven't done the math but the cross sectional area of a #4 bar (1/2" dia) at 5' might not be that different from the wire in a 6 x 6 mesh.

With that said, I probably would not space my bars more then 24" apart. It's overkill but even though I know better, I'd still do it.

Keep in mind that steel reinforcing doesn't prevent cracks nor does it add flexural strength to a 4 or 5" slab on grade. It's sole purpose is to hold the slab together across control joints or random cracks. Bars at 5' centers would probably be just fine for this purpose. Think of the money I could save if only I took my own advice.
 
OP
M

mikewatson

Well-known member
Joined
Sep 18, 2013
Messages
56
Location
sheboygan wi
Im just trying to figure out what is the rightway . my buddy does footings for the company but sees and has help do other side jobs with flate work crew . he said if it cracks you just need it to hold the sections from shifting up and down . they do 3 rebar bars 6" apart around the out side then 5' squares in the center. he doesnt know why they do it this way but that is how they do it by him .
 
Last edited:
OP
M

mikewatson

Well-known member
Joined
Sep 18, 2013
Messages
56
Location
sheboygan wi
what about using sheets of remesh 4x8x.33 comes in 6x6 squares ? would that be just as good ? as1/2 rebar on 5x5 squares ?or as good as the 1/2 rebar at 24 spacing?
 

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,378
Location
Central Maine
Mike, The bars around the perimeter of the slab are typically placed in the bottom of a thickened haunch. The haunch acts like a beam to support the weight of the structure above. The rebar in the slab within the perimeter haunch does keep the slab from "shifting up and down" if it cracks. I think your buddy is giving you pretty good advice.

Rebar is superior to mesh in that it doesn't sag as much between supports. A #4 bar is rigid enough to span supports that are 4' apart. Mesh would need to be supported every couple feet to keep it from ending up on the ground where it will do no good. The extra supports will coat more than the extra cost for the rebar.

Let me give you a couple additional things to consider;


  • Make sure you install a well compacted, granular sub base under your slab
  • Install a vapor barrier with taped seams
  • Make sure your rebar is properly supported in the middle of your slab
  • Keep the mix water to a minimum by limiting slump and/or using a mid range water reducer
  • If a random crack will ruin your day, cut some control joints 1/4 the depth of the slab.
  • Properly cure your slab for at least seven days

There's obviously more to it but if you hit these items, you'll be well on your way to a good slab. Good luck with your project.
 
Last edited:
OP
M

mikewatson

Well-known member
Joined
Sep 18, 2013
Messages
56
Location
sheboygan wi
Thanks i am build on land that has lots of clay and will compact 3-4 in of gravel over that . Im not to worryied about if it cracks, i just dont want it to shift up and down , one thing that worrys me is it will have pex in it for heat and if it shifts the pex (i would think )would crack .
 
OP
M

mikewatson

Well-known member
Joined
Sep 18, 2013
Messages
56
Location
sheboygan wi
the building is a hybrd steel web frame with wood purlins and gurts . iIwas told i could drill 4 ft concrete piers/footings ? then put up the building then pour the inside slab after that. not sure on this part yet or just do a monolithc slap
 

Krodad

Well-known member
Joined
Mar 25, 2006
Messages
304
Location
Iowa
24" OC #4 is pretty much the standard here, though some go to 48" OC.
Your floor with 2" insulation is exactly what I did, though I did not do floor heat. I'm jealous of you! What a great way to go.

Incidentally, I'll be doing another 36x 20 addition this spring, this time going to use 3" eps insulation (over vapor barrier) and helix micro reinforcement in lieu of rebar. It's incredible stuff, and the adhesion of concrete to eps creates and incredibly rigid floor.

Good luck with the project!

Sent from my SCH-I535 using Tapatalk
 
To avoid these ads, REGISTER NOW!

D3B Dave

Well-known member
Joined
Dec 13, 2008
Messages
52
Location
Missouri
I have laid more than my share of mud. All on public contracts that Engineers designed.

You have been given some sound advice, in laying a sub base of 4" thick of 1" base rock, compacted very well. A wire tied grid of #4 rebar on 18" centers, supported on rebar chairs to place it in the center of the slab thickness.

This point I can not stress enough. Make sure the rebar is on chairs to place it in the center of the slab. Don't let anyone tell you it is ok to just lay it in the forms and then pull it up in the mud as it is poured. As the mud is worked the rebar will get stepped on or gravity along with the weight of the mud will force it to the bottom where it does no good. All concrete will crack. If the rebar is in the center then the crack will remain just a very small spider webb crack with no separation or shifting. If it is in the bottom of the slab then when it cracks the rebar will bend and you have a large crack.

Saw cuts will allow the cracks to be controlled where they form. Just be sure to fill the saw cuts with a self leveling floor caulk. If you cut it when it is still green it is a lot easier. You can get creative with your pattern.

I like to use a sealer on new concrete.

Good Luck, Dave
 

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
In NY we have a similar climate to WI. I used #4 bars every 2 feet in both directions 20 years ago and the floor is still performing well.
On grade putting the bars in the center of the slab is ok because they are holding the concrete together more than adding strength. In other situations it goes in other places. Concrete is strong in compression and weak in tension; steel is strong in tension and weak in compression. If the slab spans two beams, it goes in the bottom of the slab in the span because that is where tension is and over the beams additional bars are added at the top of the slab because the top is in tension over the beam. If you have a thick slab and you can put the bars away from the center and still have adequate concrete coverage around them, put them toward the bottom to help support heavy localized loads on the floor.
 
Last edited:

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,155
Location
Chicago, IL
Im going to be pouring a 42 by 60 x4 in 5 bag mix floor, i see most people on here space rebar in 12" squares in there buildings . now my buddy say they place rebar in 5 ft squares but i dont see any one else doing this . he works for a big concrete company also . I was thinking of using mesh and rebar around where the lift would be ,but he say no just use rebar 5ft squares is all you need because if it cracks the rebar with hold it from shifting up . Iam in cental wi and will be doing infloor heat an 2in insulation under if that matters. im thinking this is incorrect doing 5ft sq's

The American Concrete Institute has calculations for this, but there are a lot of variables. Going off what other people do, may not be applicable to your situation. Some of the variables to consider:
- How much insurance you want to have against cracking outside of control or expansion joints.
- Grade of rebar/reinforcing
- Cross sectional area of rebar/reinforcing per foot of slab
- Strength of concrete
- Depth of concrete
- Types and spacing of expansion/control joints

What is your plan for expansion/control joints? How thick will your slab be? What strength of concrete are you going to go with?


I just poured a 5" 3000 psi slab, on 2" foam, with radiant tubing and had to have 7.75" squares of #4 rebar on one slab section and 9.5" squares on another. (I called for larger bars and stronger bars initially, but my contractor showed up only with #4 60KSI bar - so I had to whip out my computer and re-run the calculations. Larger, stronger bars would have made for wider spacing, but they were the ones who had to work around it and tie up all that extra rebar.)

The 7.75" was for a slab where I have no control (saw cut) joints. It's a lot of steel, but is what is called for to make the cracks (which will happen) hairline. Those will be filled in/covered by an epoxy coating later.

The 9.5" floor is what I needed for resistance cracking due to bending in my garage slab. I designed this originally for added piece of mind with my lifts and was REALLY glad I did as we went to pour the slab. I found that the 2" 60 psi foam board was so stiff that it bridged imperfections in the compacted base. So, the top of my 2" foam was anywhere from 0" to 1/2" higher than it should have been. Hopefully, this reinforcement will keep things together as the slab settles and can account for any small voids that may be left under the foam.

The 9.5" slab does have saw cut control joints, but the rebar also enabled me to stretch them out around my lift to 13.5' at the widest point.

Spacing of control/expansion joints is a game of probabilities. Cracking will happen and the trick is to use the joints as a channel to pick where they occur. The variables above impact the likelihood of cracking occurring outside of those control/expansion joints. ACI also gives tables for balancing all of these variables, but the tighter you can make them, the higher the likelihood that cracking will be limited to the joints.

If you are just doing a simple slab with normal (10' saw cut control joints) you may not need any reinforcing, at all. The reinforcing will just help steer the cracking that does happen to those control joints and will help keep any cracking that does happen narrower.


Spacing rebar at 5' seems a bit wide but it may not be as crazy as it sounds. Reinforcing in a slab is based on the cross sectional area of the reinforcing relative to the slab section. I haven't done the math but the cross sectional area of a #4 bar (1/2" dia) at 5' might not be that different from the wire in a 6 x 6 mesh.

It's around twice the steel as 10 ga. mesh, which I found surprising.


Rebar is superior to mesh in that it doesn't sag as much between supports. A #4 bar is rigid enough to span supports that are 4' apart. Mesh would need to be supported every couple feet to keep it from ending up on the ground where it will do no good. The extra supports will coat more than the extra cost for the rebar.

Let me give you a couple additional things to consider;


  • Make sure you install a well compacted, granular sub base under your slab
  • Install a vapor barrier with taped seams
  • Make sure your rebar is properly supported in the middle of your slab
  • Keep the mix water to a minimum by limiting slump and/or using a mid range water reducer
  • If a random crack will ruin your day, cut some control joints 1/4 the depth of the slab.
  • Properly cure your slab for at least seven days

There's obviously more to it but if you hit these items, you'll be well on your way to a good slab. Good luck with your project.

I agree. I did a small, non-critical, section of my slab with mesh on chairs to save some money and it was a total disaster. (It just got trampled and ended up in the bottom of the slab, anyway.) Totally worthless. Fortunately, I planned for this and have enough saw-cut control joints to deal with any cracking. If I was to do it all over again, i would have sprung for the rebar and just spaced it widely.
 
Last edited:

texas webb

Well-known member
Joined
May 26, 2012
Messages
52
Location
San Antonio Texas
All good points above.3/8" or1/2" bar on 24" centers will be fine.You can go
wider spacing but I would also use 6x6 mesh on top.Make sure you create
perimeter beams and cross beams maybe 8-12" deep.You said you have clay,
It can expand and contract with ground moisture-maybe excavate and add
compacted base.
 

racer-john

Well-known member
Joined
Apr 1, 2008
Messages
1,461
Location
Newmarket, ON Canada
As someone mentioned the re-bar is to control tension in the slab and should be about 1-1/2 to 2" from the bottom of the slab on saddles.
The 6x6x3 mesh resides in the top 1- 1-1/2" of the slab and is there to control shrinking of the slab while curing.
 

brownbagg

Well-known member
Joined
Mar 20, 2006
Messages
5,208
in reality, rebar is not needed in a slab, footer yes, but slab no, rebar is only for load factors.
 

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
My building plan called for 12" spacing #4 for a 48' x 30' x 6" monolithic slab. It also had a cage of #5 for the footers. I requested the 6" slab for my lift and heavy machinery.
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,155
Location
Chicago, IL
in reality, rebar is not needed in a slab, footer yes, but slab no, rebar is only for load factors.

Steel of some sort is required in slabs where crack control is required. (above and beyond what control joints provide)


Rebar spaced at 5' OC each way is just about the dumbest thing I've heard this week and I deal with contractors everyday all day so I hear some fantastically stupid stuff. Are you sure your so-called buddy wasn't just messing with you?

5" is perfectly fine when 6" doesn't provide enough strength and 4" is a waste of money/material. Most designers will pick even fractions of feet so only 3rd grade math skills are needed to do the work. Those numbers are a lot easier to lay out with a normal tape measure. Dividing 12 by 5 requires a little more head math to lay out, but I'd hope that most workers could pull off adding 5's. 5-10-15-20-25-30...

As pointed out above, my contractor laid my over-reinforced slab at 7.75" on center. They bitched like crazy about it but shut up whenever I pointed out that, had they brought the size of bar spec'd on the plans, they would be working with easier 10" centers.
 

nolimits76

Well-known member
Joined
Jul 11, 2013
Messages
959
Location
Oklahoma
In regards to your spacing, I'm not an engineer and won't pretend to be. That being said, I've been in construction for a long time building bridge structures and heavy commercial structures (prisons, event centers, banks, etc).

I've never seen rebar spacing on 5' centers. My own homes I've built I've never seen spaced on that large of centers. Based on what I've seen in my professional and personal life, I would not be comfortable with it even if the math worked out. For the small expense, I'd rather run #4's on 12" or 18" centers with additional reinforcing in your perimeter footings, as well as any intermediate grade beams.


the building is a hybrd steel web frame with wood purlins and gurts . iIwas told i could drill 4 ft concrete piers/footings ? then put up the building then pour the inside slab after that. not sure on this part yet or just do a monolithc slap

In bridge construction, we commonly used drilled shafts. We drill down to rock socket and set in about 5', place our rebar cage and then pour concrete. Our application is probably much different than yours. Typical diameters are 48" to 72", some up to 108"! A shallow depth would be 10' and long depths are 125'+. Obviously when you drill, you are going through existing earth so engineers typically provide us soil boring logs so we have an idea the hardness of soil (and/or rock) we may encounter when drilling. The softer it is, the faster it goes and the cheaper the price. We have specialty drill rigs we send to drill the holes and then use cranes to set rebar cages in place. Finally, concrete is pumped into place.

That's probably more info than you need or want. My point is I like drilled shaft construction because I think it provides some strength advantage. However, depending on specifics of your shafts and if you can do this with rented equipment or need to bring in truly special drilling equipment, this could become an expensive option.

Alternatively, some states use concrete or steel H-piles in combination with spread footings in lieu of drilled shafts.
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,155
Location
Chicago, IL
My building plan called for 12" spacing #4 for a 48' x 30' x 6" monolithic slab. It also had a cage of #5 for the footers. I requested the 6" slab for my lift and heavy machinery.

What was the rebar for the slab and what was the spec of the concrete strength?
 