Recep's behing "non easily movable objects"

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Puttin in boxes & recep's in the shop end of my garage, in one corner where I would like to put a box, there is a strong potential that down the road Its where I put my heating oil tank. The tank would cover that recep if I indeed place it there. Is that gonna be a problem?
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,872
Location
oregon
Not with me, I don't think the oil guy would care, but the person attempting to use the outlet may speak of your heritage if it is blocked.

lg
no neat sig line
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
the only real problem i see is if there is a problem in the box. you won't be able to get to it to repair it. if you put it in make it the end of the line so you can just abandon it if you have to.
 

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,908
Location
Walnutport PA
NEC 314.19
Junction boxes shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building.

Do you meet this requirement?
Could you access, remove the outlet, and inspect the wiring if the need arises in the future?
 

Ryf

Well-known member
Joined
Jun 8, 2012
Messages
244
Location
Southern Ohio
I would say if thats your future plan save the hassle and don't put it there, put a double box a few feet short of where you plan it will sit on each side (go measure one the size your planning on to see) and make due with a short cord if needed. I wouldn't want one there if I thought it would mean I can't get the most room possible in the room (lost real estate).

I doubt the code would be an issue unless the tank is considered permanent, akin to a refrigerator outlet behind the refrigerator or behind washer and dryers/ovens etc. the unused 220 outlet behind my gas stove would be a code violation in the same manner if this was the case.
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
NEC 314.19
Junction boxes shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building.

Do you meet this requirement?
Could you access, remove the outlet, and inspect the wiring if the need arises in the future?

Trick question..LOL. Using the equipment I have on hand, shouldnt be an issue. Not something I'd want to do every other day, but something I wouldnt loose sleep over.


I doubt the code would be an issue unless the tank is considered permanent, akin to a refrigerator outlet behind the refrigerator or behind washer and dryers/ovens etc. the unused 220 outlet behind my gas stove would be a code violation in the same manner if this was the case.

Code wise, thats what I was thinking as well...It would be easier to move the heating oil tank for me then it would be to move the bedroom set we have which blocks 2 outlets...tractor doesnt fit in the house :lol_hitti
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Regardless of code WHY bother putting it there if this is the case??? Just put it higher so it will be just above the tank later. Like 60" or so.
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
The question herein lies: "Is the oil tank part of the building?"

What criteria are we using to judge?
I'd say no, its not part of the building...its clearly "OK" to have an outlet hidden behind a massive dresser or other large furniture object.

2 guys in the house to work on that recep behind the dresser or 2 guys out in the garage to work on the recep behind the oil tank. I bet I could have the oil tank moved before the 2nd drawer of clothes is pulled out of the dresser.

As for what I'll do...I'll omit the recep, and put a 2 gang recep next to the welder outlet (as seen in my HD recep post).
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
2 guys in the house to work on that recep behind the dresser or 2 guys out in the garage to work on the recep behind the oil tank. I bet I could have the oil tank moved before the 2nd drawer of clothes is pulled out of the dresser.
HAHAHAHA...I'd take that bet.

Make wire you have unions installed on the 2" rigid black iron pipes coming out of the top of the tank. :thumbup:
 