recommend VFD for 480V 3-phase

Duct Tape Man

Well-known member
Joined
Jul 13, 2013
Messages
994
Location
Shenandoah Valley, VA
I have the opportunity to get a bench grinder that apparently was used shipboard at some time, for a screamin deal. It's a 1-1/2 HP unit, powered by 480V 3-phase. However, my shop only has 120V and 220V 1-phase. Is there any VFD you guys would recommend to power the grinder off the wall voltage I have? Or is this a lost cause?
 
To avoid these ads, REGISTER NOW!

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
You'll need a transformer to step your 240V up to 480V and a VFD. Since there are no single-phase input 480V VFDs that I'm aware of, you'll have to use around a 3 HP three-phase VFD on single-phase input.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
Check the grinder motor and see if it has a low voltage spec. If so, wire that up and get the vfd drive.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Replace the motor, it isn't cost effective to buy all the equipment just to run it on 480v.

On a grinder motor replacement is not a option but either passing on purchasing it, or see if a motor shop can bring out the leads to wire it for 240V, then a VFD could be viable. Unless the parts to run it 480V are free, it is as Aceman says not worth it, plus 480 is not DIY.
 

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
see if a motor shop can bring out the leads to wire it for 240V

This is a viable option, but will probably cost as much as a small used transformer.

If there's no particular attachment to this grinder, there are many 240V 3-phase grinders in the sub-$500 range on Ebay every day.
 