I'm getting ready to line up 4 breakers at the top of the box, two on each side, the 240 volt loads with tied handles. Then several single pole 15 amp breakers filling out the box.

The main feed at the top of the box has two large aluminum cables, black sheathing, one with a red stripe and one no stripe (black stripe ha ha). The neutral has a white stripe. I've understood that red and black doesn't matter, 240 loads are red and black, whichever.

When I see a "pretty picture" of a wired panel the 240 breakers match across from one side to the other; red, black, red, black in my case and same on the other side. Wouldn't this be "changing' colors across the breaker? To make one buss bar red and the other black, wouldn't I land the wires red, black, red, black on one side and black, red, black, red on the other?

Doesn't matter right? Is one way more **** retentive than the other?
 
To avoid these ads, REGISTER NOW!
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
Never mind. I was thinking of the buss bar tabs alternating wrongly. It is clear matching the sides IS keeping one buss bar the same color.:p
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Unless you have a clear panel cover I wouldn't worry to much about the colors matching in order,just make it neat
 
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
Yeah, I know...it only has to look neat for a couple of hours while I put it together. After that, nobody will ever see it again...:lol:
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I tend to want to keep red on one bus, and black on the other, when it comes to 240v, or MWBC. I went down the panel and using the diagram in the inside of the door which has the two bus's marked A and B. I marked the middle of the cover, between the breakers, red and black alternating. A is red (remember that Scarlet lettter? and B is..... well..... Black. The color codes carry thru, esp the MWBC I set up for the lighting. This is plug and cord Metal Halide and the switching is UP/OFF/DOWN with up being both circuits and Down just being the A or Red circuit. I labeled the receptacles at the light fixtures accordingly.

Charles

attachment.php
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
I'm getting ready to line up 4 breakers at the top of the box, two on each side, the 240 volt loads with tied handles.


You're required to have an internal trip mechanism on the 240V breakers thus 2 pole breakers.

Handle ties are used to switch multiple 120V circuits at once.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Indeed, it makes no sense to buy handle ties to connect two individual breakers, even for a MWBC where it is allowed, because the price of two individual breakers plus the handle ties is more than a double pole. Breakers are stupid cheap until you get above 60 amp, so why do it the hard way.

Charles
 
To avoid these ads, REGISTER NOW!
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
People ALWAYS get confused by the difference between a handle tie and a common trip breaker...
Well, I'm not confused exactly. I thought I was describing a 240V common trip breaker that occupies two slots in my panel. I had no idea there was a separate thing as a handle tie to put on two single poles breakers. Since I have no idea why you would do such I thing, no danger of me buying a handle tie.

Thanks for the assist. My panel is now both pretty and safe.:)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Well, I'm not confused exactly. I thought I was describing a 240V common trip breaker that occupies two slots in my panel. I had no idea there was a separate thing as a handle tie to put on two single poles breakers. Since I have no idea why you would do such I thing, no danger of me buying a handle tie.

Thanks for the assist. My panel is now both pretty and safe.:)

Handle ties are for breakers that feed MWBC/multi-wire branch circuits.

A 240v circuit NEEDS to be fed by a common trip breaker. A handle tie for this circuit is not code compliant.

Are the breakers for your 240v loads common trip or just 2 single breakers that are handle tied?
 
OP
I

Ironcrow

Well-known member
Joined
Sep 30, 2005
Messages
1,169
Location
Arizona
New question: I just found a string of 4 receptacles that switch colors at the first receptacle. Red, white and PE from the breaker to the first receptacle. The Romex leaving that receptacle is black, white, and PE daisy chained to the other three receptacles. I know this works, its been installed for decades. And there is little risk that somebody would pull a feed off the end of this string, hook it to a red phase and expect 240, getting instead 120 V. Beside making my teeth itch, is this a code problem? I can use either in the panel, right? If I felt like it I could run the entire panel, both sides in, say, black. But, can I switch horses in the middle of the stream?
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Blue isn't just for 3 phase,it can be used as a hot wire anytime. You can use any color wire in residential for a hot as long as it's not white,gray or green
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Handle ties are for breakers that feed MWBC/multi-wire branch circuits.

A 240v circuit NEEDS to be fed by a common trip breaker. A handle tie for this circuit is not code compliant.

OK, I have a question. I have a Reliance Controls 31410C manual transfer switch. It has (10) circuits- (6) 120V 15A & (4) 120V 20A circuits. All have individual "Gen/Off/Line" switches. Each switch has a push button reset breaker. The (4) 20A circuits came with (2) handle ties installed and the instructions tell you to use them for 240V 20A circuits. I am using one pair of 20A switches with a handle tie to feed my ductless mini split A/C unit. Is this a violation?



Tommy
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Not a violation,the fuses in that panel are just for when the generator is running. It's the same as a 2 pole in main panel just that panel gas each phase on the sides instead of alternating. So left side is one phase and right side is another phase
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Not a violation,the fuses in that panel are just for when the generator is running. It's the same as a 2 pole in main panel just that panel gas each phase on the sides instead of alternating. So left side is one phase and right side is another phase

I kind of thought so, but after reading about the handle ties not being the same as a common trip, I thought twice about it.

Thanks!

Tommy
 