Running 12/2 MC cable on my garage ceiling to 4 strip lights, but the knockouts are all 3/4 on the lights.

If using a reducing washer is not legal... can i just drill new 3/8 holes in the housing for the MC conduit fittings?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,788
The MC fittings should be 1/2", 3/8" are rather odd. 1/2" X 3/4" reducing washers are very common.


1/2" conduit size is 7/8" hole opening.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
MC connectors use a 1/2" conduit hole.

We use these, Arlington 38ast:
 

Attachments

  • 94c8742c-d6f0-4da2-b1a3-973db9d3cfe8_1000.jpg
    94c8742c-d6f0-4da2-b1a3-973db9d3cfe8_1000.jpg
    95.8 KB · Views: 7
OP
C

ColoradoToy91

Well-known member
Joined
Aug 13, 2014
Messages
98
Location
Roxborough, CO
The MC fittings should be 1/2", 3/8" are rather odd. 1/2" X 3/4" reducing washers are very common.


1/2" conduit size is 7/8" hole opening.

MC connectors use a 1/2" conduit hole.

We use these, Arlington 38ast:

Thank you both- what I get for trying to figure out diameter on home depots website. Do those fittings exist in 90*

Edit: Found it 851ST
 