I recently installed a new Mr. Heater Big Maxx 80,000 heater model F260560 and I am unable to change the manifold pressure.
When I started it up for the first time, the heat exchange became glowing red hot and filled my garage with a hazy smoke.
I thought maybe it was getting too much natural gas so I measured from the pressure taps and I got the following.
Inlet Pressure (Not Running): 8.4" WC
Inlet Pressure (Running): 4.3" WC
Manifold Pressure (Running): 3.7" WC
The manual states it should be pre-adjusted for natural gas already at 4.0" WC
I tried messing with the pressure adjustment screw but no matter which direction or how much I turn it, the running manifold pressure will not change from 3.7" WC.
I completely unscrewed the pressure adjustment screw to make sure it had a spring.
I'm having a hard time finding time to contact their support line during their available hours.
The heater has not glown red hot since that first run.
Is the regulator broken?
Is 3.7" close enough to 4.0" that I should be fine running it as is?
Thanks
When I started it up for the first time, the heat exchange became glowing red hot and filled my garage with a hazy smoke.
I thought maybe it was getting too much natural gas so I measured from the pressure taps and I got the following.
Inlet Pressure (Not Running): 8.4" WC
Inlet Pressure (Running): 4.3" WC
Manifold Pressure (Running): 3.7" WC
The manual states it should be pre-adjusted for natural gas already at 4.0" WC
I tried messing with the pressure adjustment screw but no matter which direction or how much I turn it, the running manifold pressure will not change from 3.7" WC.
I completely unscrewed the pressure adjustment screw to make sure it had a spring.
I'm having a hard time finding time to contact their support line during their available hours.
The heater has not glown red hot since that first run.
Is the regulator broken?
Is 3.7" close enough to 4.0" that I should be fine running it as is?