Replace a duplex recepticle

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I have a duplex receptacle on my kitchen counter, approx. 24" from the sink. It no longer will hold plugs securely when they are plugged into it. I guess it is wore out. The house is a little over 35 years old. Do I need to replace it with a GFCI? Any wiring challenges except getting the wires stuffed back into the box and of course making a brand new piece look it belongs?
 
To avoid these ads, REGISTER NOW!

HoosierMark

Well-known member
Joined
Jan 31, 2013
Messages
1,438
Location
Southeast IN
If you have the ability to add a GFI outlet, I know I would. If it is that close to the sink, it is just a good safety move. I find when replacing some outlets it is just a matter of trimming the wires back to as short as reasonably possible and then pushing, maybe a needle nose pliers to grab a wire and push it back in further. Patience is the key word for us who only do electrical work sparingly.
 

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
Is your existing plug a split circuit? If you wish to keep it as a split and have it as a gfci you will have to get a 2 pole gfci breaker, and break out the tab on the new plug.

Otherwise use only 1 circuit for your gfci outlet
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I am sure that it is a 15 amp circuit, not sure of breaker amperage. Not a split circuit. I am not able to look at box now but believe there are 2 gfci breakers. They cover the 2 bathrooms and exterior receptacles. If I put in a gfci and there is a gfci breaker is that create problems for the circuit? There is another receptacle on the other side of the sink as well.
 

jeffmattero76

Well-known member
Joined
Mar 26, 2018
Messages
115
If the circuit is protected by a GFCI breaker, then changing the counter receptacle to a GFCI is a waste. Simply replace the old duplex receptacle with a new one. If the circuit is on a regular breaker, then, yes, it would be better and would be required that the new receptacle be a GFCI.

If you do use a GFCI receptacle, the incoming cable wires should be connected to the LINE terminals, and any wires that provide power to a downstream receptacle(s), should be connected to the LOAD terminals.

Also, I believe code says that there must be a minimum of 6 inches of wire as measured from the back of the box to the end of the wire.

Sent from my SM-G530T using Tapatalk
 

jeffmattero76

Well-known member
Joined
Mar 26, 2018
Messages
115
One more clarification, since I don't know what you mean when you say "I'm sure it's a 15 amp circuit, not sure of breaker amperage". If you have 14 gauge wire, the breaker MUST be 15 amp. If you have 12 gauge wire, the breaker can be 20 amp.

Remember that the purpose of any breaker is to protect the WIRE by limiting the amount of amperage that can travel in that wire, thereby preventing a fire.

Sent from my SM-G530T using Tapatalk
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,880

20A small appliance circuits are required in kitchens. They're full of high draw appliances (toasters, microwave, hot plate, welder, blenders....), so the 20A circuit prevents blown breakers. But nothing actually has 20A plugs, so why not use 15A receptacles.
 
To avoid these ads, REGISTER NOW!

jeffmattero76

Well-known member
Joined
Mar 26, 2018
Messages
115
Because they are cheaper, and are allowed by code. Also, I have yet to see a kitchen appliance with the 20 amp plug configuration.

Sent from my SM-G530T using Tapatalk
 

Rc_Guy

Well-known member
Joined
Apr 14, 2013
Messages
4,415
Location
Minnesota
So you mean the 20 amp plug with one space sideways I assume?

Our vending trailer has all 20 amp outlets but they all are the normal looking ones.
 

jeffmattero76

Well-known member
Joined
Mar 26, 2018
Messages
115
A 20 amp receptacle has a sideways T shaped slot and a vertical slot. Any appliance that draws more than 15 but less than 20 amps would have a male plug with one horizontal and one vertical blade. However, I have yet to see any kitchen appliance with the 20 amp male plug configuration.

Sent from my SM-G530T using Tapatalk
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
20A small appliance circuits are required in kitchens. They're full of high draw appliances (toasters, microwave, hot plate, welder, blenders....), so the 20A circuit prevents blown breakers. But nothing actually has 20A plugs, so why not use 15A receptacles.

You use a welder in your kitchen? :wtf:
 
OP
A

akpolaris

Well-known member
Joined
Jun 14, 2010
Messages
214
Location
Seward, Ak
I am not home to actually look at the box / breaker.. I am working remotely, just reviewing the list of what needs looking at when I get home

One more clarification, since I don't know what you mean when you say "I'm sure it's a 15 amp circuit, not sure of breaker amperage". If you have 14 gauge wire, the breaker MUST be 15 amp. If you have 12 gauge wire, the breaker can be 20 amp.

Remember that the purpose of any breaker is to protect the WIRE by limiting the amount of amperage that can travel in that wire, thereby preventing a fire.

Sent from my SM-G530T using Tapatalk
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,313
Location
Alexandria, VA
The discussion raises a related question. Standard duplex receptacles are rated for 15 amps with 20 amp pass through, so they can be used on a 20 amp circuit. Does a typical 15 amp GFCI receptacle have the same type of rating for 20 amp pass through? So the only reason for a 20 amp GFCI is to get the 20 amp receptacle form factor, which would not be necessary in a kitchen?

Bruce
 