Unless I am mistaken, the lack of an equipment safety shutoff device in a secondary drain pan above a finished occupied space is not in compliance with the International Residential Code.
Mechanical Code has required it since 2012:
"If you are using a drain pan under the appliance, 307.2.3 paragraph 4 (Auxiliary and secondary drain systems) says:
A water-level detection device conforming to UL 508 shall be provided that will shut off the
equipment served in the event that the primary drain is blocked. The device shall be installed in the
primary drain line, the overflow drain line, or in the equipment- supplied drain pan, located at a point
higher than the primary drain line connection and below the overflow rim of such pan.
"If no drain pan or aux drain line is being used, 307.2.3.1 (Water-level monitoring devices) says:
On down flow units and all other coils that do not have a secondary drain or provisions to install a
secondary or auxiliary drain pan, a water-level monitoring device shall be installed inside the primary
drain pan. This device shall shut off the equipment served in the event that the primary drain becomes restricted. Devices installed in the drain line shall not be permitted."
Tommy