Replacement for a run capacitor-- recommended specs

larryq

Well-known member
Joined
Jul 12, 2011
Messages
2,421
I have a 1/2 HP grinder I'd like to replace the run capacitor on. I'm ordering a start capacitor and may as well get a run cap from the same place and save on shipping.

The current run capacitor is oval sized, and has a 370V rating and 6 MFD. This place only carries 5 MFD or 7.5 MFD capacitance in 370v. If I need to choose I assume the 7.5 is the way to go? Or is there a big problem not having exactly 6?
 
To avoid these ads, REGISTER NOW!

BMack37

Well-known member
Joined
Aug 28, 2015
Messages
1,091
If you go up in voltage can you get a 5MFD cap? The 7.5MFD should work but it may effect power. Having higher voltage rating is not an issue(other than size/cost). Do they also list size? Make sure it fits!
 

mikebaker1129

Well-known member
Joined
Oct 16, 2014
Messages
1,576
Location
Huffman,TX
General rule is +or- 10% on capacitance.
I would suggest you try an HVAC/ air conditioning supply ,they keep a good stock of capacitors in stock here in Houston.
You can also parallel 2 caps together, 4+2= 6 and get your desired capacitance.
 
Last edited:
To avoid these ads, REGISTER NOW!

jallyn

Well-known member
Joined
Jun 29, 2015
Messages
448
Location
Fort Wayne, Indiana
Either 5 or 7.5 MFD (micro-Farads) are close enough. But like someone else posted, there is no quality penalty for getting a higher voltage-rated capacitor that is 6 MFD as long as it physically fits. Just make sure you don't go to a lower voltage rating (it may burn up). And get as close as possible on MFD since that is what is tuned with your motor winding's impedance to give the best power and running characteristics.
 

monkeyspanners

Well-known member
Joined
May 28, 2013
Messages
419
Location
Oxford, UK
If i had to choose i would go with a lower rated uF one, many motors run for ages with capacitors that have aged and now have a lower rating without apparent harm, but i have seen a motor burn up within a week where a higher uF capacitor had been fitted.

Just get the correct one even if you have to go elsewhere and pay extra postage.
 

Davefr

Well-known member
Joined
Jan 7, 2010
Messages
11,849
Location
OR
Rule of thumb is to stay + or - 10% but I'd try and match it as close as you can. The reason is if the cap needs to be replaced down the road and it's already deviating from spec by 10%, someone else could deviate another X% and then you have a motor that's too far out of spec.

If you deviate from the OEM spec and least right somewhere on the motor what the original values were.
 
OP
L

larryq

Well-known member
Joined
Jul 12, 2011
Messages
2,421
Thanks guys. Think I'll look elsewhere for the run capacitor and stick with 6 MFD to play it safe.
 