Replacing cooktop, need to increase wire/breaker size

jumpstart

Well-known member
Joined
Jan 11, 2009
Messages
401
Location
Central MA
I need to replace the existing 40 amp breaker with a 50 amp per the instructions with the new cooktop. The also requires increasing the wire size from 8 awh to 6 awg.

The existing wire is 3 conductor. I found the white neutral is just capped in the junction box where the appliance whip is connected. Only the black and red ( conductors) and ground is needed. With the new 6 awg, can't I just use 6/2 wire?
 
To avoid these ads, REGISTER NOW!

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,322
Location
Beautiful Southern Maryland
Only the black and red ( conductors) and ground is needed. With the new 6 awg, can't I just use 6/2 wire?
I think you actually need the neutral for the 120v control circuits. The old setup was probably using the ground for neutral too. I was under the impression that all new and upgraded installations had to be 4 wire. Hopefully somebody else will verify that.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
6/2 should be fine, but it depends on whether or not the new cooktop needs a neutral, I don't recall ever seeing one that did but it's been awhile. How many wires are in the new cooktops whip?
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
I'm willing to bet that you can swap the existing 40A breaker with a 30A, use the existing conductors and crank all the burners to full heat and still not trip the 30A breaker...
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
I'm willing to bet that you can swap the existing 40A breaker with a 30A, use the existing conductors and crank all the burners to full heat and still not trip the 30A breaker...
I need to replace the existing 40 amp breaker with a 50 amp per the instructions
It's a Code violation not to follow the instructions (110.3 B)
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,838
Most cooktops years ago had 4 standard wattage burners and even 20 years ago the pigtails on GE were wired black, red, white tied to bare or green. Now cooktops may have 5 or more higher wattage burners so that is why they have the amp upgrade. I would suggest the 6/3 with G so that if that new one fails early you can meet wiring requirements for it's replacement. Appliances and everything else are not lasting like they did even 15 years ago. Its much easier to upgrade once than have to do it again 5-10 years down the road.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
In my own house I would wire it to the existing circuit and in the event it ever trips the breaker I would rewire. Good chance that never happens.

I've seen a couple of ranges wired with a 30 amp breaker and #10 wire. I asked the owners about it and they said it's never tripped.

I've measured amps on my own range and it will hit the upper 30s if you turn on all the burners and the oven. But once a couple burners or the oven warm up it's down in the 20s or even less.
 
Last edited:

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
713
Location
Southern Alberta
In my own house I would wire it to the existing circuit and in the event it ever trips the breaker I would rewire. Good chance that never happens.

I've seen a couple of ranges wired with a 30 amp breaker and #10 wire. I asked the owners about it and they said it's never tripped.

I've measured amps on my own range and it will hit the upper 30s if you turn on all the burners and the oven. But once a couple burners or the oven warm up it's down in the 20s or even less.


In my own house I would try in the existing wiring. There was a time not that long ago 2 pole 40a breakers were scarce so some stoves got a 2p 30. Haven't heard of any problems yet.

However. We could all be wrong and the new appliance will actually draw up to 45 or more amps.
 
OP
J

jumpstart

Well-known member
Joined
Jan 11, 2009
Messages
401
Location
Central MA
In my own house I would try in the existing wiring. There was a time not that long ago 2 pole 40a breakers were scarce so some stoves got a 2p 30. Haven't heard of any problems yet.

However. We could all be wrong and the new appliance will actually draw up to 45 or more amps.
I'm going to rewire and use the 50amp per manual. Manual shows max draw at 45.6amp. Probably never use it with all burners on max, but pretty easy to access wiring in basement so I'll just do it and be done.

Thanks all for the advice.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,325
Location
Alexandria, VA
You may want to run 6/3, just in case you later find an upgraded appliance you want to use in a future remodel. It's not that much more per foot, and you will be prewired for a future appliance that needs a neutral (usually because part of the appliance needs 120 volts).
 