To avoid these ads, REGISTER NOW!

Replacing kitchen windows.. Off rough opening?

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
Finished renovating my kitchen, looking to do my windows now. Almost all box stores have windows for rough opening heights of 38", which tells me that's common. My rough height is 37.25" the width is 28 which is common, but the height on 2 of them is short. Id like to avoid ordering custom windows (about 100 bucks more each) and I did find that some box stores sell them with an actual height of 37.25", which is exactly what my opening is. Should I chance it being that tight? Any way to rasp down the window say 1/8" inch or do something with the frame? These are replacement windows without a nail flange
 
To avoid these ads, REGISTER NOW!
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
Then I would well over an inch low... how would I get contact with the stop on the top of the frame? Never done windows this will be my first time.. seems simple if I can get the window size figured out lol
 

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
If you have enough room above your countertop or backsplash, remove the 2x4 at the bottom of the rough opening and substitute a 1x4.
 
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
If prefer to not open the wall or anything.. the sill is already sloped and finished.. if I get the right sized window it should be a simple remove and replace
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,000
Location
Minneapolis
Go to the store and measure the actual value of the height on their window that takes a 38" rough opening. The rough opening dimension has a little slack in it, to allow for getting the window centered and installed plumb and level.

Then, go home and check your rough opening to see how plumb and level it is. If you're lucky, there may be enough fudging factor to let the new window fit in your old opening.
 
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
They all say on their site the actual frame size. Smallest I could find was 37.25, exactly my height
 

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
A sawzall can cut the opening bigger without much issue. Get a good stiff blade and open it up as needed.
 

Tejay

Well-known member
Joined
Dec 29, 2014
Messages
105
The lintel/ header at the top may be capped with a 2x6 or 2x4 - worth investigating . That will give 3/4 more if replaced with a 1x4 like previously stated
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,325
Location
VT
If prefer to not open the wall or anything.. the sill is already sloped and finished.. if I get the right sized window it should be a simple remove and replace

?

How do you have a sill on a rough opening?

Post a pic.
 

tcianci

Well-known member
Joined
Feb 7, 2009
Messages
4,242
Location
Walpole, Ma
Guys, he's looking to install a replacement window so he has no access to the framing. OP, if you look at the construction of the replacement window, you will see that the top of the window usually has a channel type feature to it with the inner and outer edges of the window jamb being proud of the main section of the jamb. they cut down beautifully with a simple block plane.
 

alwaysFlOoReD

Well-known member
Joined
Sep 24, 2013
Messages
2,382
Location
Airdrie, Alberta, Canada
windows for rough opening

These are replacement windows without a nail flange

Terminology matters.
A "rough opening" is measured from framing member to framing member...the 2x4 inside the wall.
The "replacement windows" without a nail flange are probably "insert" windows that are meant to fit inside of the original windows' "finish" framing. The window glass is removed and any filler strips also removed leaving the carcass of the original window frame in the rough opening and then the "insert" window is placed in the hole.
If this is an insert window then you can hack the old window frame to your hearts content, making the opening big enough to fit the window. I like about 3/8" space between new and old for low expanding foam. Of course by the time you figure your time for all the hacking and then fixing so it looks good, it may be money well spent to get the custom window. It depends on your skill level.
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
Guys, he's looking to install a replacement window so he has no access to the framing. OP, if you look at the construction of the replacement window, you will see that the top of the window usually has a channel type feature to it with the inner and outer edges of the window jamb being proud of the main section of the jamb. they cut down beautifully with a simple block plane.



Not all windows are equal.

He could have a window with removable strip to to screw through on the brickmold. Replacing a window and changing the opening size usually hinge son siding type. You can usually put a taller window in with some work but not wider as the header is already set. Just order a proper sized window. Cut out what you have and if the siding is easily manipulated then measure the r.o. Size and order your window. Be a cheap *** and you'll have issues. Not install a window with less than 3/8" combined top and bottom at least. You'll be asking for trouble.


Sent from my iPad using Tapatalk Pro
 
To avoid these ads, REGISTER NOW!

tcianci

Well-known member
Joined
Feb 7, 2009
Messages
4,242
Location
Walpole, Ma
Not all windows are equal.

He could have a window with removable strip to to screw through on the brickmold. Replacing a window and changing the opening size usually hinge son siding type. You can usually put a taller window in with some work but not wider as the header is already set. Just order a proper sized window. Cut out what you have and if the siding is easily manipulated then measure the r.o. Size and order your window. Be a cheap *** and you'll have issues. Not install a window with less than 3/8" combined top and bottom at least. You'll be asking for trouble.


Sent from my iPad using Tapatalk Pro

Please reference the OP's first post... He's installing a replacement window without a nail fin. The window he is trying to use fits into the existing jamb. More than once he references the sloped sill. If you're actually interested in helping this guy, you need to read and understand the post.
Many replacement windows are constructed exactly as I have described in my earlier post. I have "re-sized" many replacement windows on site with a block plane. It's a less than perfect world out there and sometimes things need to be modified.

This is certainly a thread that Zeke needs to weigh in on.
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
Please reference the OP's first post... He's installing a replacement window without a nail fin. The window he is trying to use fits into the existing jamb. More than once he references the sloped sill. If you're actually interested in helping this guy, you need to read and understand the post.

Many replacement windows are constructed exactly as I have described in my earlier post. I have "re-sized" many replacement windows on site with a block plane. It's a less than perfect world out there and sometimes things need to be modified.



This is certainly a thread that Zeke needs to weigh in on.



Have you installed a replacement window without a nail fin that has a removable strip brick mold? There is no reason this would not work? Much better of a seal and cleaner look then installing a window inside of the old ones frame. I thought I was helping....with my experience as a builder.


Sent from my iPad using Tapatalk Pro
 
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
I'm sorry my terminology isn't correct, as every so how window I have looked at that installs the way I'm talking is called a "replacement window" on every box stores website.

Tcianci:
Is there usually enough to take off 1/4 To 1/2" with a plane?

Also I found this window...
https://m.lowes.com/pd/ThermaStar-b...n-x-36-75-in-Actual-27-5-in-x-36-5-in/3119105

It's short... now I've never installed a window but I remember an old buddy installing one once, and his was too short but came with an extension that went on the top, like a cap, to fill the space... do windows usually come with these? Because I would only have to make up about 3/8-1/2 inch to get a good deal against the top stop
 

850xpeps

Well-known member
Joined
Aug 6, 2017
Messages
1,365
It's all good. Replacement windows up here can mean either ones with removable strip on brick mold or the ones you referenced. If it were mean I'd never install that in replacement to the type with an jntegrated brick mold. Just my preference.


Sent from my iPad using Tapatalk Pro
 

tcianci

Well-known member
Joined
Feb 7, 2009
Messages
4,242
Location
Walpole, Ma
I'm sorry my terminology isn't correct, as every so how window I have looked at that installs the way I'm talking is called a "replacement window" on every box stores website.

Tcianci:
Is there usually enough to take off 1/4 To 1/2" with a plane?

Also I found this window...
https://m.lowes.com/pd/ThermaStar-b...n-x-36-75-in-Actual-27-5-in-x-36-5-in/3119105

It's short... now I've never installed a window but I remember an old buddy installing one once, and his was too short but came with an extension that went on the top, like a cap, to fill the space... do windows usually come with these? Because I would only have to make up about 3/8-1/2 inch to get a good deal against the top stop

The window in your link sounds like it would fit your opening. "Short" is a relative term. The window installs against a feature of the old window called the blind stop. If your new window is tall enough to overlap onto the blind stop of the head jamb, you're in good shape. If it doesn't quite make it, then you would use the head expander.

Replacement (insert) windows are usually supplied with 2 accessories, the terminology of either may vary by region. The 2 accessories are the sill extender and the head expander. The sill extender is just that, a piece plastic that fits onto the bottom outside rail of the window to allow the window to fit along the sloped sill of the old unit. When installed, the new window is essentially resting on the inner bottom rail and the bottom edge of the sill extender. Sill extenders are nominally sized for window sill with a slope of 14 or 15 degrees. Some manufacturers, like Andersen, actually ask for the sill slope when you order windows from them.
Some sill extenders are simply a vertical piece of plastic that snaps into a groove in the face of the bottom rail of the window and these extenders can be cut for a sill of shallow slope. Other sill extenders have an additional feature at the bottom that gives the extender more contact area against the sill and helps the extender to stay rigid. They too can be cut but the rigidity of the extender could be compromised.
The other accessory is the head expander, It is a vinyl channel that slips over the top rail of the window and it takes up any extra space between the top rail of the window and the head jamb of the old window. We typically insulate the voids at the sill extender and the head expander to optimize the efficiency of the window.
It sounds like in your case, you would be installing the window without the head expander since height is an issue. As I previously mentioned, the top edges of many replacement windows are raised above the main body of the rail itself and this feature can be trimmed off. It is however, unlikely that there's more than 1/4 of an inch to be had in this area. If you were to trim this feature at the inner and outer edges of the top rail of the window and the same feature at the inner edge of the lower rail and a corresponding amount from the bottom edge of the sill extender, it may be possible to "shrink" the window by about 3/8".
At this point you may understand why several have advised you to spring for the custom sized window. However, if your handy and adventurous, you may save yourself a few hundred bucks.
 
Last edited:
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
The window in your link sounds like it would fit your opening. "Short" is a relative term. The window installs against a feature of the old window called the blind stop. If your new window is tall enough to overlap onto the blind stop of the head jamb, you're in good shape. If it doesn't quite make it, then you would use the head expander.

Replacement (insert) windows are usually supplied with 2 accessories, the terminology of either may vary by region. The 2 accessories are the sill extender and the head expander. The sill extender is just that, a piece plastic that fits onto the bottom outside rail of the window to allow the window to fit along the sloped sill of the old unit. When installed, the new window is essentially resting on the inner bottom rail and the bottom edge of the sill extender. Sill extenders are nominally sized for window sill with a slope of 14 or 15 degrees. Some manufacturers, like Andersen, actually ask for the sill slope when you order windows from them.
Some sill extenders are simply a vertical piece of plastic that snaps into a groove in the face of the bottom rail of the window and these extenders can be cut for a sill of shallow slope. Other sill extenders have an additional feature at the bottom that gives the extender more contact area against the sill and helps the extender to stay rigid. They too can be cut but the rigidity of the extender could be compromised.
The other accessory is the head expander, It is a vinyl channel that slips over the top rail of the window and it takes up any extra space between the top rail of the window and the head jamb of the old window. We typically insulate the voids at the sill extender and the head expander to optimize the efficiency of the window.
It sounds like in your case, you would be installing the window without the head expander since height is an issue. As I previously mentioned, the top edges of many replacement windows are raised above the main body of the rail itself and this feature can be trimmed off. It is however, unlikely that there's more than 1/4 of an inch to be had in this area. If you were to trim this feature at the inner and outer edges of the top rail of the window and the same feature at the inner edge of the lower rail and a corresponding amount from the bottom edge of the sill extender, it may be possible to "shrink" the window by about 3/8".
At this point you may understand why several have advised you to spring for the custom sized window. However, if your handy and adventurous, you may save yourself a few hundred bucks.

Thank you so much for your help! That window I posted isn't custom but is special order at lowes... I'll swing out there tomorrow and see if they can tell me if it comes with the head expander or not. It seems it would be the easiest option if it does. I'll also see how much material is on them that can be taken off... thanks again!!!

As for installation... from what I've gathered is it's pretty straight forward... pull the old Windows out, clean every thing, caulk on the stops, set the window and square it, and caulk every seam I see... sound abiut right?
 

73RR

Blank Email
Joined
Dec 13, 2016
Messages
300
Location
Central Ory-Gun
I have read through this thread and have not found where you tell us exactly the vintage of the structure, what type of window you have, or what type of wall construction. No photos?
Terminology does indeed vary across these fruited plains and with me on the West coast I often get confused by NE descriptions however, you do not indicate where you are located so perhaps others are also confused.
I have replaced multiple hundreds of windows but still not sure how to offer any suggestions as I really don't know what you have......
 
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
Iowa, 1976 house.. no pics right now. Typical wood windows with metal tracks in the center of the frames on the sides... has outside stops at the top and sides.. that's of the top of my head
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Having helped with replacing the windows in our house, TCI has it. Measure the opening, order a window. Spend the $$$, otherwise you'll be screwing with fitment and seal. Not worth it on what amounts to a huge hole in the side of a house. If you want to save $, wait for HD to run one of their 15% all custom door and window sales.
 
OP
S

Sh40674

Well-known member
Joined
Jan 8, 2014
Messages
1,428
Location
Iowa
I'm going to Lowe's in a bit to check on the pella window I posted.. they don't have that exact size, but they have others from that line there. If they have that expansion cap on the top I think I'll go that route. They're 27.5 wide and 36.5 tall, if I can get even close to 1/2" extra with that cap it should fit just fine. Thanks everyone!
 

Steven K

Member
Joined
Oct 9, 2011
Messages
21
I have been down the same road many times with non standard sized windows. I found that shopping around at door and window supply companies got me a better price than the box stores for a custom size.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Another vote for NOT buying a ready made off the shelf window....

And another vote for TCI's input.

I just replaced my kitchen window....
Of course, be being the typical GJ member.....well....I didn't take the easy route....

Took out the old 36x36 POS....opened things up a bit...ordered custom windows...Milgard...fiberglass on the outside (it means I can paint them), vinyl inside, low E, double paned, Argon filled. Side windows are casement so we can crank them open.

I'm in the process of making new cabinets. The granite will actually go into the bay window area.
 

Attachments

  • IMG_4592.jpg
    IMG_4592.jpg
    148 KB · Views: 8
  • IMG_4732.jpg
    IMG_4732.jpg
    140.8 KB · Views: 6
  • IMG_4744.jpg
    IMG_4744.jpg
    141.7 KB · Views: 8
  • IMG_4741.jpg
    IMG_4741.jpg
    139 KB · Views: 7

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,989
Location
West central Indiana
Find a local glass dealer that sells okna or sunrise Windows. They custom make every window(no "stock" sizes) for about 2/3 the cost of stock andersons/pella/Marvin. They are better built as well.
 