Replacing Lift - What to do with old holes?

gte610v

Member
Joined
Jul 10, 2012
Messages
20
Has anyone ever replaced a lift with another one? How did you guys deal with the old hole pattern? Is this a cut out and re-pour or can you fill the holes and relocate semi-close to the old footprint?
 
To avoid these ads, REGISTER NOW!

Diesel Dan

Well-known member
Joined
Jul 21, 2013
Messages
2,460
Location
TN
Drive the old studs through the slab, if possible, so they are about 1" down. Fill hole with s-mortar or non shrinking grout.

If they are bottomed out cut flush with floor.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Has anyone ever replaced a lift with another one? How did you guys deal with the old hole pattern? Is this a cut out and re-pour or can you fill the holes and relocate semi-close to the old footprint?

Define semi-close?

The correct answer is to check with the manufacturer of the new lift you are installing... follow their specifications.
 

Nexussian

Well-known member
Joined
Mar 12, 2014
Messages
639
Location
Alaska
How far off is the new bolt pattern?

What kind of anchors were in the old holes?

If the new holes overlap, and the old anchors are a "wedge" type, I might look to see if I could replace them with a "drop in" or epoxy type anchor that was bigger enough around that I could grind the holes to fit.

Anything more than half a hole off though, and that likely won't work. :(

I'm no engineer, but I might risk that.
 
Last edited:

Warrenator

Well-known member
Joined
May 31, 2008
Messages
781
Location
Newberg, OR
In my wife's old factory there were quite a few semi-protruding sawed off bolts sticking up through the concrete from old equipment casually removed. I used a zip disc on a 4 1/2" grinder to cut them off flush. They become just a spot in the concrete after a while, you don't notice them.
 
To avoid these ads, REGISTER NOW!

8man

Well-known member
Joined
Oct 16, 2013
Messages
630
Location
Bryan, Texas
Stress on the concrete from a 2 post lift is different than with a 4 post lift.

4 post, do as advised above.

2 post lift, contact the factory for advice. You may need to cut out, retie steel and re-pour, that is a safety measure that may be required.
 
Last edited:

BFBOB

Well-known member
Joined
Sep 20, 2011
Messages
5,073
Sell 'em on eBay - "Lift Installation Kit" :lol:

......Acme brand, of course



edit --- I just read the posts. I'd assumed the hole in question was a big one for an in-floor lift. For those little bolt holes, don't bother. They wouldn't bring enough to be worth the shipping.
 
Last edited:

rattle_snake

Well-known member
Joined
Jun 25, 2015
Messages
5,213
Location
Chandler, AZ
Has anyone ever replaced a lift with another one? How did you guys deal with the old hole pattern? Is this a cut out and re-pour or can you fill the holes and relocate semi-close to the old footprint?

Most concrete anchors have tension spec (the one you care about) de-rated when installed in proximity to an edge, crack or another hole. The specs and de-rating are published by the anchor manufacturer, so this is what you need to determine your situation.

Typical mechanical (wedge, drop in , screw in) need about 12" from anything. However the spacing between the anchors themselves in the base plate is less than that, more like 6". So the 'critical distance' from any new hole to an old hole is roughly equal to the bolt to bolt spacing of the baseplate.

If you want the new 2 post lift post in the same location as the old, you will most likely need to re-pour. It doesn't matter what you do with the old holes, the concrete is already compromised.
 
Last edited:

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Typical mechanical (wedge, drop in , screw in) need about 12" from anything. However the spacing between the anchors themselves in the base plate is less than that, more like 6". So the 'critical distance' from any new hole to an old hole is roughly equal to the bolt to bolt spacing of the baseplate.

Edge distance, for a Rotary 2 post, is specifed as 4-1/2", using Hilti Kwik Bolt III's: http://www.rotarylift.com/Support/FAQ/.

But epoxy anchors are more forgiving. They don't stress the concrete like mechanical anchors and they require no minimum nut torque, since they are chemically bonded to the concrete and don;t require nut pre-load to lock the anchor.

The OEM of the lift may well recommend epoxy anchored studs if the new holes are indeed in close proximity to the new holes.

I wanted to use epoxy on my Rotary, and called the factory. They supplied the specification via email.
 