Hey everyone. I had a problem with my ac unit so I reset the main breaker to the house and now all the power is still out. Is there a certain sequence to turn on breakers? I don't turn them on or off ever. Please help. It's 101 outside and 90 inside. Thank you.
 
To avoid these ads, REGISTER NOW!

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,925
Location
Northern Central Ohio
Are your neighbors without power ?

Turn the main off. Do you smell anything ? If you do, you may want to call your local fire dept.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,925
Location
Northern Central Ohio
Wait a minute. I reread the post. There was no need to reset the main. Turn the main off, turn all the other breakers off. Turn the main back on, then turn the smaller breakers back on one at a time ?

Do you have an up to date service ? 100 or 200 amp service ? Or is it a 60 amp service with 30 amp fuzes screwed in everywhere ?
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
The neighbors have power. Everything was working fine before I flipped switches. No burning smells. I don't consider myself very smart on things like this, but its just a breaker switch. The power should be working. Is there anything special to flipping on and off the main power and the individual switches? Any particular sequence?
 

Strouty

Well-known member
Joined
Mar 21, 2010
Messages
38,215
Location
Southern Maine
Did you pay your bill? I would think that the main would just turn back on once you flip it. Is there a disconnect outside? Did the main actually trip from the AC or did you turn off the main to fix the problem? Good luck.
 

jrevans

Well-known member
Joined
Jun 29, 2009
Messages
78
Try this.

Turn the main breaker off. Make sure the handle on the breaker travels all the way to the off position, Then move the breaker to the on position. you should feel some resistance when turning it on.

let us know if this works

Jim
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
Lol. Yah paid the bill. I couldn't find a switch on the ac. So i tried to find the breaker switch.
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
I turned off main. Then turned off all the smaller ones. Turned back on the main. Then the smaller ones. Still no power. What the Hell? Could there be something I'm missing here? Everything was working fine except the ac unit before i switched anything.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,925
Location
Northern Central Ohio
How old is the breaker box ? What kind is it ? Hopefully not a federal Pacific. It might be something such as the main has taken a ****.
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
I just turned off the main. Turned it back on. Felt resistance and heard a click. Still no power. Idk what's going on.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,925
Location
Northern Central Ohio
Do you feel capable enough to remove the cover off the breaker panel ?



I believe GE had some breaker panels made by Siemens, I think I heard they had a problem with the aluminum bussbar melting. I could be wrong here.

You may want to be calling an electrican soon.
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
I took off the breaker panel. Nothing looks melted. I can't find any other box inside the house. Could it be possible for there to be a trip switch inside the oge box located right next to breaker box? The elec co. Has a lock on it.
 

JeremyManning

Well-known member
Joined
Oct 12, 2010
Messages
1,457
Location
Ontario, Canada
I would call the electric company and have them check their end, let them know that you have checked your end to no avail, let them check their end before calling an electrician, unless you have a buddy that is an electrician.
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
Trying to upload pics
 

Attachments

  • IMAG0585.jpg
    IMAG0585.jpg
    149.2 KB · Views: 184
  • IMAG0586.jpg
    IMAG0586.jpg
    139.6 KB · Views: 219

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
That little panel is for your whole house? I'd like to talk to the guy that installed that, talk about leaving no room for wiring additional items later on!

Get a multimeter and see if there is power on the meter side of the hots.
 
To avoid these ads, REGISTER NOW!

slice

Well-known member
Joined
Jun 16, 2010
Messages
331
your main is not all the way off make sure the switch goes far right then turn it back on
 

rhdave

Member
Joined
Jun 17, 2010
Messages
20
Location
Edmonton, AB
Looks like the meter is displaying something, that means you should have power from the supply authority.

Look at the handle on the main breaker, it looks crooked. You may have to turn it off, then back on making sure both poles engage.

Calling the supply authority won't cost you anything, they'll come have a look and make sure everything's fine from their end.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
I would bet guaging the age of that panel and the fact that its an outdoor panel " I hate those " your main breaker just took a **** :D. I would at this point call a qualified electrician and have him come out and change the main breaker tell him over the phone its an older GE 100 amp main and he should be able to bring one with him.


Rick
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
your main is not all the way off make sure the switch goes far right then turn it back on


Actuallly going back and having a second look Slice is right you need to push the main all the way to the left and then all the way back to the right if you still dont have power then your main took a **** and you need a new main breaker .


Rick
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
Well elec co just showed up. I'll let ya know what happened.

Edit: well elec co just left. He said that their end is good. He said it seems to be something tripping that main 100 breaker or its bad.
 
Last edited:

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
Get a multimeter and see if there is power on the meter side of the hots.


Right! You can flip breakers the rest of your life, or you can troubleshoot the problem. Pull the cover off your main panel if you are capable of doing it without killing yourself. IF NOT, CALL AN ELECTRICIAN!!
Then take your meter and measure the voltage coming in. If it is OK, measure the voltage after your main breaker, and keep going until you find the problem.

Or, keep flipping breakers. It doesn't matter what order you flip breakers. The end result is the same.
 

Carl B

Well-known member
Joined
Feb 3, 2006
Messages
525
Location
Clearwater, Florida USA
Could be as simple as the Time Delay on the A/C unit. When you lose power - there is usually a 10 minute Time Delay at the compressor. As long as you keep flipping switches/brakers - it keeps resetting the A/C Time Delay.

Leave the power on - and wait to see if the compressor comes back on..

FWIW,
Carl B.
 

Carl B

Well-known member
Joined
Feb 3, 2006
Messages
525
Location
Clearwater, Florida USA
Second place to look is at the compressor - there should be a quick disconnect there - many of the disconnects are of the Fused Type. Usually with two time delay 20 0r 30 amp fuses.

If it is a fused type disconnect - then simply change the fuses.

FWIW,
Carl B.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,925
Location
Northern Central Ohio
When you try resetting the main, make sure the other breakers are off.


I'd also hope that you have a gas stove and gas dryer ?
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
Reset the main and left the other ones off. I'll see if they work when I come back. If not then I'm.guessing I will have to call an electrician. Any idea how much that could run if its as simple as a main breaker? And I'm guessing i wouldn't want to try to mess with it myself?
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,925
Location
Northern Central Ohio
Cost, don't know, but the electrican may want the power company back out there to pull the meter, unless he likes to live dangerously.
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
Well I have an electrician coming out.. lesson learned. Don't flip switches.lol. need to do something. Its 108 today in okc.
 
OP
I

Incubus21

Member
Joined
Jul 3, 2011
Messages
13
Alright. Everything is back on. Electrician came out and replaced main breaker. Now I'm back to where I started. My ac is still not running. The unit in the back yard is making a humming noise. The fan isn't spinning. Any ideas? Thank you to everyone that helped with my elec problem. I was in a panic. It's nice to know there are sites like this one with friendly and helpful people.
 

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
Your best bet is to call an HVAC service and if they can come out tomorrow, do that. The likelihood that a homeowner can do much of anything is pretty low. And I don't mean to sound like a ****, but the likelihood that you can fix the HVAC but couldn't troubleshoot your breaker is basically zero.

Try to get the power to the HVAC killed (so the humming stops and any further damage, however unlikely, is minimized). Kill it via a service disconnect, by the AC's breaker, or by turning off the T-stat. Open some windows and hope you can get service tomorrow.

If you want to troubeshoot further, start with determining if the air handler fan is working. Does air move in the house (even if it's HOT air)? If not, you may have a fighting chance, because that fan may be within your ability to fix or replace. If that fan is running and the outside unit (condenser) is not working, you're pretty much screwed.

I'd wager you're screwed because the air handler fan (the first one I talked about) would be unlikely to take out the house electrical if it failed, while the AC condenser might be more likely to do so.
 

slice

Well-known member
Joined
Jun 16, 2010
Messages
331
a/c is humming becasue the capacitor in it just " blew up" you need a new one,, and it only happens on july 4th weekend,. yea i play electrician and a/c guy..... good luck...
 

mikeatrpi

Well-known member
Joined
Jan 10, 2006
Messages
383
Location
Home
a/c is humming becasue the capacitor in it just " blew up" you need a new one,, and it only happens on july 4th weekend,. yea i play electrician and a/c guy..... good luck...

This happened to me. My compressor outside would hum and the fan would run inside the house but the air was not being cooled. With the disconnect OFF - I took the panel off the a/c outside and found a melted wire and bulging cap. I shorted its leads with a screwdriver (no spark - it was discharged already) and took it out. Ended up buying a new cap at the local a/c place for $20ish and making a replacement wire.

If you're handy enough to use some common sense and be safe, it wouldn't hurt to pull the panel off and take a look inside. Maybe you also have a blown cap?
 