Just got my Reznor hung and plumbed, everything look ok?


65762ac4.jpg


2fd80ed6.jpg
 
To avoid these ads, REGISTER NOW!

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
Looks good from what I can see except maybe your choice of electrical feed/cable. It's hard to see from the pic but that looks like some sort of rubber jacketed cable. It really should have more protection.
 

Wackerjr

Well-known member
Joined
Sep 29, 2010
Messages
103
correct me if I am wrong... but shouldnt the T on the gas line be fed from the top, Drip leg on the bottom, and feeding the unit from the side.... that way everything that "may" come out of the line shoots past the opening instead of directly in the heater...
 
To avoid these ads, REGISTER NOW!
OP
S

stuntman

Member
Joined
Oct 4, 2009
Messages
22
I dont think you're wrong.
Should be easy enough to correct.
Thanks for the feedback so far.
 

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
The use of the SO cord maybe ok if your local codes permit. Should be hard wired but if not at least a twist-lock plug.

Not sure how your shop is set-up and abit late now but the heater should blow warm air towards the area that is least insulated (Garage doors, windows etc..). By the picture it is on the same side as your garage door (unless you have another one on the other side).
 