A couple weeks ago, we noticed the house feeling colder than usual, checked the thermostat. It was set to 70, but inside temp was 66. We set to emergency heat (propane, not electric resistance) until we could get it sorted.
i found the 3a fuse for the control circuit on the indoor unit open. It immediately (within 3 seconds) blows when regular heat is selected.
the reversing valve reads 16 ohms. The contactor control circuit reads 15 ohms.
if I press in the contactor, the outdoor fan runs. After releasing the contactor, I can hear gas equalizing, so I believe the compressor is also running. The 2 LEDs on the outdoor unit control board blink together. That means everything is ok according the table on the board itself.
I shotgunned an outdoor unit control board with no luck. The LEDs on both boards have the steady blink.
I had a soft start unit installed on it to help with starts when running on generator power, but I’ve removed that to eliminate that as a possibility.
i think now it is either the RV solenoid or the contactor. Note this is a rheem unit, so the RV solenoid is energized when calling for heat unlike other brands.
i Removed the Thermostat and jumped the contacts for fan and RV to the 24v power. The fuse blew.
I replaced the fuse and selected ac on the thermostat. The fuse blew.
my belief now is the contactor is drawing too much current, despite ohming at a reasonable level.
any other ideas?
i found the 3a fuse for the control circuit on the indoor unit open. It immediately (within 3 seconds) blows when regular heat is selected.
the reversing valve reads 16 ohms. The contactor control circuit reads 15 ohms.
if I press in the contactor, the outdoor fan runs. After releasing the contactor, I can hear gas equalizing, so I believe the compressor is also running. The 2 LEDs on the outdoor unit control board blink together. That means everything is ok according the table on the board itself.
I shotgunned an outdoor unit control board with no luck. The LEDs on both boards have the steady blink.
I had a soft start unit installed on it to help with starts when running on generator power, but I’ve removed that to eliminate that as a possibility.
i think now it is either the RV solenoid or the contactor. Note this is a rheem unit, so the RV solenoid is energized when calling for heat unlike other brands.
i Removed the Thermostat and jumped the contacts for fan and RV to the 24v power. The fuse blew.
I replaced the fuse and selected ac on the thermostat. The fuse blew.
my belief now is the contactor is drawing too much current, despite ohming at a reasonable level.
any other ideas?