Riser Schedule Q

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
I'm running two conduits between the house and the garage.

One is for data. The 2nd is for a 12-2 light switch run.

I have not found anything that provides guidance on the type of risers that I need to come out of the ground and into the sill plates of the house or garage.

(called AHJ, but nothing back yet...)

I suppose the safe answer is to run rigid metal down to the 18" cover depth, then schedule 40.
 
To avoid these ads, REGISTER NOW!
OP
S

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
For the record it needs to be Schedule 80 PVC, RMC or IMC. But it is a subjective call by the AHJ on how much damage the riser can be subjected too.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
Needs to be schedule 80 where subject to damage! And FYI- the power for the light switch circuit needs to originate from the subpanel in the garage!!
 
To avoid these ads, REGISTER NOW!