Can I run romex in my exposed garage ceiling or does the ceiling wiring need to be in a conduit?
Requires same protection as Romex. Generally, Romex on the ceiling is not subject to physical damage, and that's all that the code requires.Run MC cable
Please cite the code reference....No exposed Romeo. Run MC cable or conduit.
Please cite the code reference....
BTW MC cable has the same physical protection requirements as NM so i dont understand why youre saying to run exposed MC in place of exposed NM....
In reply to your comment that was deleted, the code is a permissive one, if it doesnt say you cant, then you can. So, there is no code that i can cite for you that says NM can be exposed. It simply doesnt exist... now this doesnt mean you cant run exposed NM however... since there is no code that specifically says "you cannot install exposed NM-b." So you wouldnt be able to cite a code that says that either....
the only code you'll find pertaining to this is that NM and MC cant be subject to damage, which is very open to interpretation and subjective.
Its been allowed to be installed exposed since it came out, per the NEC as long as certain provisions are met. But local AHJ's can always override the NEC.In the 2017 NEC, accepted installation of exposed nonmetallic cable (Romex) is covered in Article 334.
We are not allowed to have romex exposed in omaha in unfinished areas,that's been a local code as long as I can remember.Please cite the code reference....
BTW MC cable has the same physical protection requirements as NM so i dont understand why youre saying to run exposed MC in place of exposed NM....
In reply to your comment that was deleted, the code is a permissive one, if it doesnt say you cant, then you can. So, there is no code that i can cite for you that says NM can be exposed. It simply doesnt exist... now this doesnt mean you cant run exposed NM however... since there is no code that specifically says "you cannot install exposed NM-b." So you wouldnt be able to cite a code that says that either....
the only code you'll find pertaining to this is that NM and MC cant be subject to damage, which is very open to interpretation and subjective.
Can't say for Indiana specifically but in most cases it can be run along the side of the joists and through holes in the joists. Not on the underside. If the hole through will be close to the edge it will need a metal protection plate just where it does through the hole.Here is a picture of the ceiling and I’m in Indiana
Pardon my ignorance, so each jurisdiction has different service rules not a statewide code ?It's already been stated, but check the local building department if you are concerned about it. I work in about seven different jurisdictions. One says everything in an unfinished has to be in conduit. One says as long as it's run within a foot of the walls when perpendicular to the joists, romex is ok. The rest don't care as long as it's not underneath the joists.
In this case, it's not really a different set of rules. It's interpretation of the term "protected from damage". It would be another thread, but there are cases of different jurisdictions having a different set of rules that they have adopted as local ordinances that deviate from the norm. The norm being what is required by the NEC, which right now is most of the 2020 NEC.Pardon my ignorance, so each jurisdiction has different service rules not a statewide code ?
we used to be that way here in Australia and it differed from one side of the road to the other 7 county councils, with 7 sets of rules . It was scraped in 89 and we went to a state wide uniform set of service rules .
and over here what you call Romex we call TPS , thermoplastic sheathed . And like you we can have clipped exposed in some parts of the shed and conduit for mechanical protection. ( we mainly use pvc conduit over Emt ) Love reading your comments. Regards A