Romex in conduit indoors?

2000xpsd

Well-known member
Joined
Feb 25, 2013
Messages
69
Location
SE Mass
Found a couple of threads on this but no clear answer... I'm wiring my flouresant lights in, they are connected with 1/2" metal conduit, can I run 12/2 to connect them all or does it have to be thhn?
I know you can't when it in a wet location but this is indoors so I need a code expert. I've got plenty of 12/2 romex, doesn't make sense to buy 3 rolls of thhn if I don't have too.
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Ive sleeved romex in conduit to protect it going down a wall wall joists,or to sleeve a piece of existing romex coming through a floor to get it to a junction box or fixture.
From that point to the next junction through a piece of conduit I would run it in thhn.
Why are you using 12/2 to feed lights?;)
 

joecam

Member
Joined
May 8, 2011
Messages
11
In NJ it is apparently a code violation to have jacketed romex in a conduit, I just had to rerun all my garage wiring with thhn.

Sent from my SM-T810 using Tapatalk
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
My experience with 12-2 in 1/2 conduit is that if you have a run of any length, you'll be wishing it was 3/4.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
A semi-related question.

Why is it improper to glue sections of PVC conduit together with the wiring already in it?

Does the cleaner or cement screw up the wire covering or cement it to the conduit?

Bill
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,939
Location
Central New Jersey
In NJ it is apparently a code violation to have jacketed romex in a conduit, I just had to rerun all my garage wiring with thhn.

Sent from my SM-T810 using Tapatalk

I live in NJ. Have lived here all my life (51 years), and I have never heard of this code violation. And I have bought and sold a few homes over the years, had them all inspected by professional inspectors, and not once did any of them ever question romex in conduit where it needed to be in it.

As a matter of fact, they all said it would be code violation if the romex was NOT put in conduit where it was exposed to any outside forces that could damage it, such as going down the surface of a wall to a wall mounted box or fixture.

The romex dropping down to the boxes in my current garage all had to be sleeved in some type of protective conduit instead of just running exposed down the walls to the boxes. Same for the wiring in my basement bar area. The inspector never said I had to rip out everything and re-do it all with individual wires. Just put the exposed romex in some conduit to protect it from damage.

It was the same for any outside UF-B wiring that was run into the ground. We had to put the UF-B in conduit where it was exposed coming out of the house and down to the ground, and up from the ground up to any box on an out building to protect it from getting damaged.

Do you have the actual code they said you violated to make you re-do your installation? That just does not sound right that you had to re-do everything with individual wires versus running any exposed romex in conduit.

Jim
 
Last edited:

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,939
Location
Central New Jersey
A semi-related question.

Why is it improper to glue sections of PVC conduit together with the wiring already in it?

Does the cleaner or cement screw up the wire covering or cement it to the conduit?

Bill

Maybe they don't want the wires to get "glued" to the conduit. If it did, it would then be impossible to pull it out if you had to replace the wires.

Jim
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
A semi-related question.

Why is it improper to glue sections of PVC conduit together with the wiring already in it?

Does the cleaner or cement screw up the wire covering or cement it to the conduit?

Bill

Because the NEC specifies that conduit is to be completely assembled before wire is installed. No reason is given in the code.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
Because the NEC specifies that conduit is to be completely assembled before wire is installed. No reason is given in the code.

Rules without reasons are meaningless. And meaningless rules create distrust of the entire body of rules and the rule making body itself.

As a practical matter, does anyone know what the thinking behind this rule is?

Bill
 

Beemer533

Well-known member
Joined
May 9, 2014
Messages
2,057
Location
Syracuse, NY
If I had to guess it would be the concern of the primer and/or adhesive damaging the conductors... But that is speculation on my part, although I can't think of anything else..
 
Last edited:
To avoid these ads, REGISTER NOW!

simpler=better

Well-known member
Joined
Oct 6, 2015
Messages
499
Location
Baltimore, Maryland
Rules without reasons are meaningless. And meaningless rules create distrust of the entire body of rules and the rule making body itself.

As a practical matter, does anyone know what the thinking behind this rule is?

Bill

The rule makes perfect sense: If you can't pull the wire through when fully assembled, you might as well have just used direct bury, or 'Romex', or BX, etc.



The reasons for using conduit instead of assembled wire thingies:
#1-Keep the wire from getting smashed, chewed, cut, rubbed, burned, etc.
#2-Allow for easy wiring changes between point A and point B after everything is said and done.
#3-Contain sparks/arcs/heat/fire/bad juju if the wiring somehow fails catastrophically inside the conduit.

Assembled cables don't do any of those very well. (Okay, #3 can be argued to a point with BX).


EDIT: The primer/glue for PVC would at least weaken the romex's insulation, if not melt through immediately. Those are some nasty solvents.

Don't mean to sound snippy, but there's a reason for using romex and a reason for using conduit..and a reason for sometimes using both.
 
Last edited:

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
^ ^ ^ ^ ^ +1.

Just put pull string in sticks of conduit when they are glued together and you won't risk damaging the wire. Once it's all glued together just yank through the wire with your pull string.

Worst case scenario, you now have pull string glued into place !! ;)

It's just better to **** through pull string with "mouse" and shop vac.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I live in NJ. Have lived here all my life (51 years), and I have never heard of this code violation. And I have bought and sold a few homes over the years, had them all inspected by professional inspectors, and not once did any of them ever question romex in conduit where it needed to be in it.

As a matter of fact, they all said it would be code violation if the romex was NOT put in conduit where it was exposed to any outside forces that could damage it, such as going down the surface of a wall to a wall mounted box or fixture.

The romex dropping down to the boxes in my current garage all had to be sleeved in some type of protective conduit instead of just running exposed down the walls to the boxes. Same for the wiring in my basement bar area. The inspector never said I had to rip out everything and re-do it all with individual wires. Just put the exposed romex in some conduit to protect it from damage.

It was the same for any outside UF-B wiring that was run into the ground. We had to put the UF-B in conduit where it was exposed coming out of the house and down to the ground, and up from the ground up to any box on an out building to protect it from getting damaged.

Do you have the actual code they said you violated to make you re-do your installation? That just does not sound right that you had to re-do everything with individual wires versus running any exposed romex in conduit.

Jim
I think hes talking about running romex in pipe from box to box versus shielding a piece of it like I was talking about.I shouldve mentioned earlier I remove the outer sheathing when I shield a piece of romex inside of pipe to a box.
Electrical inspectors frown on running it from box to box around here also.
As far as home inspectors calling it out as a violation Ive never met one that could cite an electrical/hvac or plumbing code even if you left the book in front of them open to the page.:spit:
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Rules without reasons are meaningless. And meaningless rules create distrust of the entire body of rules and the rule making body itself.

As a practical matter, does anyone know what the thinking behind this rule is?

Bill

No. They are telling you, do it this way. The book would need to be 10x as long if they had to splain why at every turn. They don't care to splain it every way to every one so they all understand it in their own personal way.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
As a practical matter, does anyone know what the thinking behind this rule is?
Bill,,, is it really that much of a stretch to imagine a slob with hot plastic cement and plastic coatings on wires. Its another thing they have found to be so they try to prevent dumb fuks from doing. Similar to not putting multiple N wires under screws, using staples and box connectors.
Its a rule regarding the workmanship and method.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I see some old jobs from 3o's. The installer must have spent an apprenticeship back then before moving to a small town along with the electric.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Does it really need an explanation to say bury it 18 or 24 and easier to allow some exceptions under certain conditions. About the only thing that has been fundamentally changed in my lifetime in the area is allowing gfci protected circuits at a foot. Some of these code and methods been in place a long time.
Protect the wire, where to drill and staple and how big some fuses need to be and some fundamental wire sizes been around since they invented the light bulb. Today with eco codes we can have more stuff with slightly less peak over a bit more time.
Not so many 1800 watt heaters out there like chore heaters of past or like a large oven on a dedicated.
Many moons ago a guy got scalded in a shower if someone flushed. Today the same pipe that was barely adequate in 1970 can feed 2 baths and never notic it, low flow shower and a stool that uses 1/4 the water over the same or longer time frame. Water slam isn't the issue it was. Most home owners are not filling tanks or irrigating and the object isn't to use as much as they can.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
A 20A is ideal for the fact that the loads in residential come thru a 15 end and it gives a bit of head room for a lamp and motor starts without nuisance trips.
 