Charles, conductor fill doesn't apply to sleeves used for physical protection.
The reference is in the Notes to Tables #2 on the first page of Chapter 9.
but for it to be a sleeve it cant be connected to a box at either end (or can it?)
Charles, conductor fill doesn't apply to sleeves used for physical protection.
The reference is in the Notes to Tables #2 on the first page of Chapter 9.
Charles, conductor fill doesn't apply to sleeves used for physical protection.
The reference is in the Notes to Tables #2 on the first page of Chapter 9.
but for it to be a sleeve it cant be connected to a box at either end (or can it?)
I have run ROMEX in conduit. In my opinion, it's safe under some conditions.
However, it is not compliant according to code: NEC 310.120
All conductor and cables shall be marked...
Technically, the ROMEX would need to be stripped AND it would need to be labeled THHN for it to be compliant.
I have run ROMEX in conduit. In my opinion, it's safe under some conditions.
However, it is not compliant according to code: NEC 310.120
All conductor and cables shall be marked...
Technically, the ROMEX would need to be stripped AND it would need to be labeled THHN for it to be compliant.
The only time you can run romex in conduit is when you are dropping it from a protected area to a non-protected (but needs to be protected) area. For example, if you had a finished ceiling in your basement but didn't have finished walls, and you were putting in a new hot water heater, code would allow you to run romex in the ceiling, and then into conduit running down to a disconnect. And any time you go from outside of conduit to inside of it you need to make sure you have the proper fittings on the end. In the example above where the transition isn't inside a junction box, there would need to be a fitting with a cable clamp to prevent the cable from rubbing on sharp edges as it transitions into the conduit.
The reason for the code is that Romex has an extra layer of insulation, so the code gods are worried about overheating it in an enclosed space (conduit). If you look at specs though, type NMB Romex (any romex made in the last 15 years) and THHN have the same temperature ratings. Also, romex is run in insulated walls which would lead me to believe the "enclosed space" argument is a moot point. Still, it's a good idea to cover your **** and use THHN.
Sorry, but you and jkeyser14 ARE NOT "spot on". You are both incorrect.You are spot on. I just mentioned that in another post.
It is a moot point. The reason they don't let you use it is that they have never tested it. Why??? Who knows. It is just one of those dumb things that falls betweent he cracks. It goes back to the more woven covering on wires from 80 years ago. The old coverings cought on fire when over heated. I guess they just carried it over to the new wiring. I have used romex for 40 years in conduit. I just strip the outer covering way back so no one can see what I have used. I never do that on a job but only in my own shops and barns.
When I sign a contract I don't take any short cuts.
You can always cut all the outer covering off and use the wires without it.
I figure if the outlet matches the breaker and you have the right size wire for the run the breaker will over heat and trip. The wire should not catch fire unless the breaker does not trip. Bad breakers don't always trip.
Remember that the codes are only a minimum standard. There is no reason to go over board when it comes to electical. Just follow the charts and you will be just fine.
Sorry, but you and jkeyser14 ARE NOT "spot on". You are both incorrect.
I'd REALLY like to know where you guys are getting all this false information. Obviously not from the NEC.![]()
I use these little puppies when pulling Romex into conduit.
![]()
Perfect for the top of a run of conduit such as a basement wall for cable protection for wall switches, outlets, etc.
This is a case (in my non professional opinion) where the romex becomes a system and not a protective sleeve. You have properly terminated the conduit on both ends, a box and receptacle or switch on one end, and the conduit to romex clamp on the other, thus a complete "system".
Indeed. The combination of the clamp, the length of conduit and the device box is more like a single "unit." It's like buying a device box with a nice, long telescopic "clamp" at the other end.
Another aspect not touched upon, if running wire (Romex or individual conductors) through a long vertical run of conduit, There is a certain point at where the wires have to be clamped at the upper end. The weight of the wiring can pull and strain the splices or junctions at the top of the run. I'm not sure at what length this comes into play, but it is an aspect to high-rise and tower wiring standards. It's a good idea to put a clamp like this when running Romex down a long run of conduit to save the weight of the cable itself from causing the cable to catch the edge of the conduit or fitting.
A friend of mine that used to be a site engineer for a few radio stations had climbed up a tower to refit the beacon lighting there. When he opened up the junction box and began to fiddlefuss with the wiring inside, the wiring coming up through the conduit below suddenly disappeared. The weight of the wires (which were probably nothing more than 14 or 12ga. THHN) caused them to slip a good distance down the conduit and birdnested in the big junction box below.
After reading this reply from Greatbear. I thought he was describing my life almost 5 years ago when I was on top of a 800 foot comm tower.
Went up to replace a relay and had to unplug a few wires. No sooner when I disconnected the blasted thing the wire just went ****!
I was right pissed!
Teken . . .



Ya deserved it - no one in his right mind would be on the top of an 800 foot tower!![]()