Quick question - is it true that you cannot run Romex (12/2) inside EMT or PVC conduit? Are individual THHN wires the only way to run inside conduit?
It's true that can not run romex in EMT or PVC but there are other types of wires that you can run in them, THWN and others.
Where in the code book does it say I can't run Romex in conduit?
If 24" or less, & indoor* not a problem, but for longer lengths why bother? More work then it's worth....
I have about 60' of wall with no outlets I need to string up...Yeah, I'm just mad because I can only buy it in 500' rolls and I need 5 colors. I DON'T need 2500' of wire, but I also don't want to pay $0.24/foot either...Still, it's a good idea to cover your **** and use THHN.
The only time you can run romex in conduit is when you are dropping it from a protected area to a non-protected (but needs to be protected) area. For example, if you had a finished ceiling in your basement but didn't have finished walls, and you were putting in a new hot water heater, code would allow you to run romex in the ceiling, and then into conduit running down to a disconnect. And any time you go from outside of conduit to inside of it you need to make sure you have the proper fittings on the end. In the example above where the transition isn't inside a junction box, there would need to be a fitting with a cable clamp to prevent the cable from rubbing on sharp edges as it transitions into the conduit.
The reason for the code is that Romex has an extra layer of insulation, so the code gods are worried about overheating it in an enclosed space (conduit). If you look at specs though, type NMB Romex (any romex made in the last 15 years) and THHN have the same temperature ratings. Also, romex is run in insulated walls which would lead me to believe the "enclosed space" argument is a moot point. Still, it's a good idea to cover your **** and use THHN.
I can see the argument - you can buy 250' of 12-2 for under $50 (last time I looked) and a single 500' spool of black runs you $122 at Grainger. Not on most peoples budget.
Lowes has 500 ft spool of THHN, 12 ga solid, all colors, for $50 a spool. I think HD is about the same.
Charles
And any time you go from outside of conduit to inside of it you need to make sure you have the proper fittings on the end. In the example above where the transition isn't inside a junction box, there would need to be a fitting with a cable clamp to prevent the cable from rubbing on sharp edges as it transitions into the conduit.
Exactly the situation I'm facing. I'll either run Romex in conduit or build an enclosed raceway to protect the NM-D until it goes up into the attic.
Do you have a link to the type of fitting you're describing?
I understand if using a junction box you would run the conduit into the JB, pull the NM-D through the conduit, into the and out of the JB, and use a standard fitting like that for entering into a load center where the Romex comes out of the junction box into the attic space. Right?
You guys are making up NEC code..
I can pull Romex in a mile long conduit all day long as long as I size it right. There is no extra "derating" for Romex. Until you guys post something factual(NEC code article), I'm calling BS.
Some folks seem to think that there local amendments should apply to everyone, well, they don't. Let's stick to what the NEC has to say about it...
This site is fantastic! Thanks guys.
Maybe I'm not looking hard enough, but I haven't been able to find the bushings or one of those cap/clamp things in my usual shopping spots.


I spent many years pulling romex through both emt and pvc for yard lights and water wells, some many hundreds of feet. I sure did get by with a lot of inspections somehow if there is anything in the NEC prohibiting such installations.
You guys are making up NEC code..
I can pull Romex in a mile long conduit all day long as long as I size it right. There is no extra "derating" for Romex. Until you guys post something factual(NEC code article), I'm calling BS.
Some folks seem to think that there local amendments should apply to everyone, well, they don't. Let's stick to what the NEC has to say about it...
Its less than 9 current carrying conductors so it shouldn't be a problemOkay, I'm running 3 12-2 (welder, compressor, outlets- each on a 20 amp breaker) and 1 14-2 (lights - 15 amp breaker) in romex in EMT conduit, tell me what size conduit to use, or if I can even do it.
Okay, I'm running 3 12-2 (welder, compressor, outlets- each on a 20 amp breaker) and 1 14-2 (lights - 15 amp breaker) in romex in EMT conduit, tell me what size conduit to use, or if I can even do it.
I am adding a couple of outlets to my garage. I will be using a 5' section and a 9' section of 1/2" EMT (for wire protection) to drop from the ceiling of my garage for 2 outlets. Can I put "2" 12/2 w/grd romex thru 1/2" EMT?
And buy a single black roll of thhn and then tape the ends red or white to save money over buying different colored rolls.