umm what? do you use the urban legend code book?
the NEC does not prohibit NM-b in raceway
the only place that NM-b cannot go is outside, whether its in raceway or surface mounted or underground.
BTW Romex is NOT a type of cable. it is a ® and ™ brand of Southwire
You guys crack me up. I never said Romex was prohibited in EMT?
I stated
"Doesn't the helper know that Romex (in
most cases but especially
this one) in EMT is illegal?"
Tell me how its possibly to code to have
5 Romex cables in a 1" tube and remain with the fill tables?
Fill for 3 plus conductors is limited to 40 percent in Chapter 9 table two.
Fill for 2 conductors is 31 percent
Fill for 1 conductors is 53 percent
Multiconductor cables for fill calculations use the largest dimension (or width) to calculate the fill percentage.
For 12/2 Romex per southwires side this dimension is .422. That would allow 2 Romex circuits in a 1" emt, 1 Romex in a 3/4 emt, and 1 Romex in a 1/2" EMT
Unfortunately many people will try to stuff more NM cables in these conduits because its possible with THHN conductors. This is why Romex/NM-B/NM-C should be discouraged in conduits of any kind as it doesn't allow for expansion very well in the future and therefore cost the customer more in the long run.
As for the civil discourse of this forum, I understand asking one to explains one position or cite sources. I would be happy, as I did above, to cite sources. However you and others jumped to tear down others.
In your case it amazes me that you go out of your way to point out that Romex is a brand name. Yet that is the term that the OP used and no such comments to him. What position am I in to question the OP as to what brand he used.