Hopefully this is a simple question. How many Romex cables is 1/2inch EMT designed or allowed to contain? It looks like adding a third cable might be too tight of a squeeze.
Thank you
Thank you
I'm not an electrician, but I don't believe that Romex is designed or intended to be installed in emt. You can run individual wires and there are web sites that can tell you how many wires a 1/2-inch, 3/4-inch etc. emt will safely hold.
Ray
PS: https://www.google.com/search?q=emt...9j69i57j0l4.8796j0j7&sourceid=chrome&ie=UTF-8

Hopefully this is a simple question. How many Romex cables is 1/2inch EMT designed or allowed to contain? It looks like adding a third cable might be too tight of a squeeze.
Thank you
342.22 Number of Conductors
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.
334.2 Definitions
Nonmetallic-Sheathed Cable. A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket.
NM-B is not approved for wet locatiions, even in conduit.
Simple answer: none.
You are better off bringing the NM-B to a box and stranded or solid wires from there into your conduit.
There are a number of reasons not to run Romex in a conduit although technically it is allowed in dry locations (inside). But to run more than one cable is just not a sound practice.
This is inside my garage, all the drops from the ceiling of my garage (block construction) to the switches/outlets are in EMT (metal conduit).
I am looking to add an outlet where there is a 2 gang box with 2 Romex cables to both switches there. I will change out the box to a 3 gang.
I'm not an electrician so are you saying my existing setup - Romex cables (in some places 2 cables) in EMT on block walls - is not recommended?
If not I'm curious as to why?
Thank you
342.22 Number of Conductors
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.
334.2 Definitions
Nonmetallic-Sheathed Cable. A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket.
NM-B is not approved for wet locatiions, even in conduit.
I think most people are missing the fact that this is not a complete conduit system and simply a sleeve for the wire were it comes down the cement wall. OP please correct me if this is not the case.
This is extremely common with any exposed concrete wall with wood framing above and perfectly acceptable.
I would absolutely not splice the romex and run thhn just a few feet down to the switch/outlet.
In regard to the original question, 3 12/2 cables physically will not fit in a 1/2 conduit.
I'm not sure of the exact rule for this since I think it differs from the standard conduit fill calculations. I was under the impression that only 1 12/2 was allowed in 1/2 but I have nothing to back that up. I have many times ran 2 12/2's through 1/2 conduit though...
All correct. Just one addition to this. Romex is not round. For conduit fill calculations, the major diameter (the widest part) must be used in the calculations, not the minor diameter (the narrowest part).
Knowing this, and assuming that Romex is 1/2" wide, the Romex works out to a cross sectional area of 0.196" (again, because code considers the circular cross sectional area of a cable, and not the actual cross sectional area). A 1/2" trade sized EMT conduit has a cross sectional area of 0.30 sq-in. A single cable is allowed to fill 53% of the conduit area (the fill percentage DROPS when more than one cable is considered), which is 0.16 sq-in, so the number of Romex cables allowed in a 1/2" conduit is ZERO.
Considering a 3/4" EMT conduit, it works out to ONE Romex per 3/4" conduit is perfectly allowed, but two or more would exceed the fill table requirements. For 1" EMT, two Romex cables would meet the 31% fill requirements for two cables, but three would exceed the 40% fill for three or more cables, so the answer is that TWO would be allowed in 1" EMT.
Turns out this is an understatement. Kinda like when I was learning to surf even the “little waves” would wipe me out.Simple answer: none.
Follow the code I referenced above for conduit sizes. Romex in conduit is fine.
I have the same situation. Bill
Romex is often installed in conduit for mechanical protection, just like you have in your garage.
It is permitted by Code.
It's permitted by code to run Romex in conduit, the conduit just has to be sized appropriately. You go by the largest cross section dimension of the Romex, then use that number along with one of the many conduit sizing programs available online to determine what diameter conduit is required.
Do yourself a favor and just buy THHN wire. Unless you have a really short run Romex is a ***** to pull through conduit. Just my experience.... I just pulled 30' with bends of THHN in 1/2" conduit for my heater today. Easy peasy.
All correct. Just one addition to this. Romex is not round. For conduit fill calculations, the major diameter (the widest part) must be used in the calculations, not the minor diameter (the narrowest part).
Knowing this, and assuming that Romex is 1/2" wide, the Romex works out to a cross sectional area of 0.196" (again, because code considers the circular cross sectional area of a cable, and not the actual cross sectional area). A 1/2" trade sized EMT conduit has a cross sectional area of 0.30 sq-in. A single cable is allowed to fill 53% of the conduit area (the fill percentage DROPS when more than one cable is considered), which is 0.16 sq-in, so the number of Romex cables allowed in a 1/2" conduit is ZERO.
Considering a 3/4" EMT conduit, it works out to ONE Romex per 3/4" conduit is perfectly allowed, but two or more would exceed the fill table requirements. For 1" EMT, two Romex cables would meet the 31% fill requirements for two cables, but three would exceed the 40% fill for three or more cables, so the answer is that TWO would be allowed in 1" EMT.
L5wolvesf,
I found these helpful...
https://www.garagejournal.com/forum/showthread.php?t=53919
http://forums.mikeholt.com/showthread.php?t=86048
See chapter 9 table note# 2. Fill restrictions for cable only apply to complete conduit systems. Not intended to apply to sections of conduit used to protect exposed wiring from physical damage.
.............. This pic is the conduit that comes into my garage and the Romex goes from here to the various switches and outlets. It has at least 10 cables, in 1 1/4inch EMT, it physically protects the Romex cables. It seems o be tightly packed’ It is about 6 ft tall from the top (in the pic) to where it goes out through the block wall into the meter/circuit breaker box.
Hopefully this is a simple question. How many Romex cables is 1/2inch EMT designed or allowed to contain? It looks like adding a third cable might be too tight of a squeeze.
Thank you
But common sense dictates there is a limit to how much romex / wire you should cram into a conduit... right? [QOUTE]
That reply was to address Bert’s comment about not sure where the exact rule is. So I reference that for him.
Even with that exception noted, I further qualified the practicality of it ......'Physically fitting the cables in is a limiting factor and the time it takes makes larger obviously the smarter choice.' So, yes we agree.
This comment was to address rlitman's conduit fill example that although is correct, it pertains to complete conduit system installation vs. incidental protective sleeves as is the context of this thread.
But common sense dictates there is a limit to how much romex / wire you should cram into a conduit... right?
Which leads us to this......
Well, you have already had a great explanation by rlitman above about the NEC rules for EMT fill volumes with Romex.
Furthermore we know the NEC has rules about bundling, unless the cable is derated.
So logically the code has a problem with wires being together as such. (possibly due to over heating due to the crowded condition?). That same logic would also seem to apply what you are showing.
But.. it depends on when the installation was done, and what was in the NEC at that snapshot in time, and if any updates have been done to your installation.
If you are updating, my understanding is whatever you update has to meet the current code.
Just running things in conduit once in a while to project wires close to machines, I'd not run any "romex" in 1/2" because it's too small unless it's like one cable going 2 or 3 feet straight. Any bends, fergetit. 3/4 min and that's for one. Maybe two if you flatten them out and tape together for the run. And I'd not count on getting anything else in there later even with a pull string.
If it were me, I would try to come close to the rules for an end to end conduit, even though this is just a case of protecting exposed Romex. It would make easy installation too.