Romex in EMT

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
Hopefully this is a simple question. How many Romex cables is 1/2inch EMT designed or allowed to contain? It looks like adding a third cable might be too tight of a squeeze.

Thank you
 
To avoid these ads, REGISTER NOW!
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
I'm not an electrician, but I don't believe that Romex is designed or intended to be installed in emt. You can run individual wires and there are web sites that can tell you how many wires a 1/2-inch, 3/4-inch etc. emt will safely hold.

Ray

PS: https://www.google.com/search?q=emt...9j69i57j0l4.8796j0j7&sourceid=chrome&ie=UTF-8


I'm obviously not an electrician either. But all the drops from the ceiling of my garage to the switches/outlets are in EMT (metal conduit).

Thanks for the fill charts - didn't know anything like that existed. :beer:
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
342.22 Number of Conductors
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.

334.2 Definitions
Nonmetallic-Sheathed Cable. A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket.

NM-B is not approved for wet locatiions, even in conduit.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Hopefully this is a simple question. How many Romex cables is 1/2inch EMT designed or allowed to contain? It looks like adding a third cable might be too tight of a squeeze.

Thank you

Simple answer: none.

You are better off bringing the NM-B to a box and stranded or solid wires from there into your conduit.

There are a number of reasons not to run Romex in a conduit although technically it is allowed in dry locations (inside). But to run more than one cable is just not a sound practice.
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
342.22 Number of Conductors
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.

334.2 Definitions
Nonmetallic-Sheathed Cable. A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket.

NM-B is not approved for wet locatiions, even in conduit.

This is inside my garage, all the drops from the ceiling of my garage (block construction) to the switches/outlets are in EMT (metal conduit).


Simple answer: none.

You are better off bringing the NM-B to a box and stranded or solid wires from there into your conduit.

There are a number of reasons not to run Romex in a conduit although technically it is allowed in dry locations (inside). But to run more than one cable is just not a sound practice.

I am looking to add an outlet where there is a 2 gang box with 2 Romex cables to both switches there. I will change out the box to a 3 gang.

I'm not an electrician so are you saying my existing setup - Romex cables (in some places 2 cables) in EMT on block walls - is not recommended?

If not I'm curious as to why?

Thank you
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
This is inside my garage, all the drops from the ceiling of my garage (block construction) to the switches/outlets are in EMT (metal conduit).




I am looking to add an outlet where there is a 2 gang box with 2 Romex cables to both switches there. I will change out the box to a 3 gang.

I'm not an electrician so are you saying my existing setup - Romex cables (in some places 2 cables) in EMT on block walls - is not recommended?

If not I'm curious as to why?

Thank you

Follow the code I referenced above for conduit sizes. Romex in conduit is fine.

I have the same situation.

Bill
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
22,994
Location
Minneapolis
It's permitted by code to run Romex in conduit, the conduit just has to be sized appropriately. You go by the largest cross section dimension of the Romex, then use that number along with one of the many conduit sizing programs available online to determine what diameter conduit is required.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,579
Location
Long Island
342.22 Number of Conductors
The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.

334.2 Definitions
Nonmetallic-Sheathed Cable. A factory assembly of two or more insulated conductors enclosed within an overall nonmetallic jacket.

NM-B is not approved for wet locatiions, even in conduit.

All correct. Just one addition to this. Romex is not round. For conduit fill calculations, the major diameter (the widest part) must be used in the calculations, not the minor diameter (the narrowest part).

Knowing this, and assuming that Romex is 1/2" wide, the Romex works out to a cross sectional area of 0.196" (again, because code considers the circular cross sectional area of a cable, and not the actual cross sectional area). A 1/2" trade sized EMT conduit has a cross sectional area of 0.30 sq-in. A single cable is allowed to fill 53% of the conduit area (the fill percentage DROPS when more than one cable is considered), which is 0.16 sq-in, so the number of Romex cables allowed in a 1/2" conduit is ZERO.

Considering a 3/4" EMT conduit, it works out to ONE Romex per 3/4" conduit is perfectly allowed, but two or more would exceed the fill table requirements. For 1" EMT, two Romex cables would meet the 31% fill requirements for two cables, but three would exceed the 40% fill for three or more cables, so the answer is that TWO would be allowed in 1" EMT.
 

mrramsey

Well-known member
Joined
Sep 23, 2016
Messages
261
Location
North East Ohio
Do yourself a favor and just buy THHN wire. Unless you have a really short run Romex is a ***** to pull through conduit. Just my experience.... I just pulled 30' with bends of THHN in 1/2" conduit for my heater today. Easy peasy.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,694
Location
NW Iowa
I think most people are missing the fact that this is not a complete conduit system and simply a sleeve for the wire were it comes down the cement wall. OP please correct me if this is not the case.

This is extremely common with any exposed concrete wall with wood framing above and perfectly acceptable.
I would absolutely not splice the romex and run thhn just a few feet down to the switch/outlet.

In regard to the original question, 3 12/2 cables physically will not fit in a 1/2 conduit.
I'm not sure of the exact rule for this since I think it differs from the standard conduit fill calculations. I was under the impression that only 1 12/2 was allowed in 1/2 but I have nothing to back that up. I have many times ran 2 12/2's through 1/2 conduit though...
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,848
Location
NJ
I think most people are missing the fact that this is not a complete conduit system and simply a sleeve for the wire were it comes down the cement wall. OP please correct me if this is not the case.

This is extremely common with any exposed concrete wall with wood framing above and perfectly acceptable.
I would absolutely not splice the romex and run thhn just a few feet down to the switch/outlet.

In regard to the original question, 3 12/2 cables physically will not fit in a 1/2 conduit.
I'm not sure of the exact rule for this since I think it differs from the standard conduit fill calculations. I was under the impression that only 1 12/2 was allowed in 1/2 but I have nothing to back that up. I have many times ran 2 12/2's through 1/2 conduit though...

See chapter 9 table note# 2. Fill restrictions for cable only apply to complete conduit systems. Not intended to apply to sections of conduit used to protect exposed wiring from physical damage.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,848
Location
NJ
All correct. Just one addition to this. Romex is not round. For conduit fill calculations, the major diameter (the widest part) must be used in the calculations, not the minor diameter (the narrowest part).

Knowing this, and assuming that Romex is 1/2" wide, the Romex works out to a cross sectional area of 0.196" (again, because code considers the circular cross sectional area of a cable, and not the actual cross sectional area). A 1/2" trade sized EMT conduit has a cross sectional area of 0.30 sq-in. A single cable is allowed to fill 53% of the conduit area (the fill percentage DROPS when more than one cable is considered), which is 0.16 sq-in, so the number of Romex cables allowed in a 1/2" conduit is ZERO.

Considering a 3/4" EMT conduit, it works out to ONE Romex per 3/4" conduit is perfectly allowed, but two or more would exceed the fill table requirements. For 1" EMT, two Romex cables would meet the 31% fill requirements for two cables, but three would exceed the 40% fill for three or more cables, so the answer is that TWO would be allowed in 1" EMT.

1/2" can be used. See chapt 9, table note# 2. Physically fitting the cables in is a limiting factor and the time it takes makes larger obviously the smarter choice.
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
Simple answer: none.
Turns out this is an understatement. Kinda like when I was learning to surf even the “little waves” would wipe me out.


Follow the code I referenced above for conduit sizes. Romex in conduit is fine.

I have the same situation. Bill

Romex is often installed in conduit for mechanical protection, just like you have in your garage.

It is permitted by Code.

It's permitted by code to run Romex in conduit, the conduit just has to be sized appropriately. You go by the largest cross section dimension of the Romex, then use that number along with one of the many conduit sizing programs available online to determine what diameter conduit is required.

When I first asked the question it was just about the Romex physically fitting – maybe it still does. I thought there might be a simple answer. Now I know the EMT in this situation is “for mechanical protection” and that it might have to be sized according to the Code too.


Do yourself a favor and just buy THHN wire. Unless you have a really short run Romex is a ***** to pull through conduit. Just my experience.... I just pulled 30' with bends of THHN in 1/2" conduit for my heater today. Easy peasy.

This is an add on to existing wiring and will be a short pull on a drop down. I also have a load of Romex from the prior owner. Wouldn’t want to pull what you described.


All correct. Just one addition to this. Romex is not round. For conduit fill calculations, the major diameter (the widest part) must be used in the calculations, not the minor diameter (the narrowest part).

Knowing this, and assuming that Romex is 1/2" wide, the Romex works out to a cross sectional area of 0.196" (again, because code considers the circular cross sectional area of a cable, and not the actual cross sectional area). A 1/2" trade sized EMT conduit has a cross sectional area of 0.30 sq-in. A single cable is allowed to fill 53% of the conduit area (the fill percentage DROPS when more than one cable is considered), which is 0.16 sq-in, so the number of Romex cables allowed in a 1/2" conduit is ZERO.

Considering a 3/4" EMT conduit, it works out to ONE Romex per 3/4" conduit is perfectly allowed, but two or more would exceed the fill table requirements. For 1" EMT, two Romex cables would meet the 31% fill requirements for two cables, but three would exceed the 40% fill for three or more cables, so the answer is that TWO would be allowed in 1" EMT.

Thank you for this. The Romex I have is 3/8inch wide and the marking on it (hard to read) looks like it says 14, it has 1 black, 1 white, and 1 copper conductor.

Every drop in my garage is 1/2inch and most have one Romex cable.
 
To avoid these ads, REGISTER NOW!
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
QUOTE=Bert_;6814168]I think most people are missing the fact that this is not a complete conduit system and simply a sleeve for the wire were it comes down the cement wall. OP please correct me if this is not the case.

This is extremely common with any exposed concrete wall with wood framing above and perfectly acceptable.
I would absolutely not splice the romex and run thhn just a few feet down to the switch/outlet.

In regard to the original question, 3 12/2 cables physically will not fit in a 1/2 conduit.
I'm not sure of the exact rule for this since I think it differs from the standard conduit fill calculations. I was under the impression that only 1 12/2 was allowed in 1/2 but I have nothing to back that up. I have many times ran 2 12/2's through 1/2 conduit though...[/QUOTE]

You are correct on what I am trying to do. It looked iffy now I know it won’t go. Thank you.

Since the right way to do it is in larger conduit I could step it up to 3/4inch – correct? Also, is the grey PVC acceptable in my situation and is grey PVC allowed to be connected to metal 3 gang switch boxes?
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ

Thank you, they are but they raise another question.

This pic is the conduit that comes into my garage and the Romex goes from here to the various switches and outlets. It has at least 10 cables, in 1 1/4inch EMT, it physically protects the Romex cables. It seems o be tightly packed’ It is about 6 ft tall from the top (in the pic) to where it goes out through the block wall into the meter/circuit breaker box.
 

Attachments

  • EMT into garage.jpg
    EMT into garage.jpg
    73.5 KB · Views: 64

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
See chapter 9 table note# 2. Fill restrictions for cable only apply to complete conduit systems. Not intended to apply to sections of conduit used to protect exposed wiring from physical damage.

But common sense dictates there is a limit to how much romex / wire you should cram into a conduit... right?

Which leads us to this......

.............. This pic is the conduit that comes into my garage and the Romex goes from here to the various switches and outlets. It has at least 10 cables, in 1 1/4inch EMT, it physically protects the Romex cables. It seems o be tightly packed’ It is about 6 ft tall from the top (in the pic) to where it goes out through the block wall into the meter/circuit breaker box.

Well, you have already had a great explanation by rlitman above about the NEC rules for EMT fill volumes with Romex.

Furthermore we know the NEC has rules about bundling, unless the cable is derated.

So logically the code has a problem with wires being together as such. (possibly due to over heating due to the crowded condition?). That same logic would also seem to apply what you are showing.

But.. it depends on when the installation was done, and what was in the NEC at that snapshot in time, and if any updates have been done to your installation.

If you are updating, my understanding is whatever you update has to meet the current code.
 

Attachments

  • EMT into garage.jpg
    EMT into garage.jpg
    103.8 KB · Views: 29
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Hopefully this is a simple question. How many Romex cables is 1/2inch EMT designed or allowed to contain? It looks like adding a third cable might be too tight of a squeeze.

Thank you

Just running things in conduit once in a while to project wires close to machines, I'd not run any "romex" in 1/2" because it's too small unless it's like one cable going 2 or 3 feet straight. Any bends, fergetit. 3/4 min and that's for one. Maybe two if you flatten them out and tape together for the run. And I'd not count on getting anything else in there later even with a pull string.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,848
Location
NJ
But common sense dictates there is a limit to how much romex / wire you should cram into a conduit... right? [QOUTE]

That reply was to address Bert’s comment about not sure where the exact rule is. So I reference that for him.

Even with that exception noted, I further qualified the practicality of it ......'Physically fitting the cables in is a limiting factor and the time it takes makes larger obviously the smarter choice.' So, yes we agree.
This comment was to address rlitman's conduit fill example that although is correct, it pertains to complete conduit system installation vs. incidental protective sleeves as is the context of this thread.
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
But common sense dictates there is a limit to how much romex / wire you should cram into a conduit... right?

Which leads us to this......


Well, you have already had a great explanation by rlitman above about the NEC rules for EMT fill volumes with Romex.

Furthermore we know the NEC has rules about bundling, unless the cable is derated.

So logically the code has a problem with wires being together as such. (possibly due to over heating due to the crowded condition?). That same logic would also seem to apply what you are showing.

But.. it depends on when the installation was done, and what was in the NEC at that snapshot in time, and if any updates have been done to your installation.

If you are updating, my understanding is whatever you update has to meet the current code.

Garage was built in '97, before the house in '98. I believe it "had to" have been inspected since the main electric meter is on the other side of the wall in that pic.

I plan on doing the additional outlet correctly which is the reason for the questions.

Thank you
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
Just running things in conduit once in a while to project wires close to machines, I'd not run any "romex" in 1/2" because it's too small unless it's like one cable going 2 or 3 feet straight. Any bends, fergetit. 3/4 min and that's for one. Maybe two if you flatten them out and tape together for the run. And I'd not count on getting anything else in there later even with a pull string.


The run I would be doing is going to be about 3 - 4 ft tall and straight until it does a slight bend before going into the switch box.
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
I also wouldn't lose sleep over a piece for protection. All this is different for heavily loaded equipment etc.

No I'm not going to lose sleep over it. There will be some added load since I'm adding an outlet, but no heavy equipment. Thank you
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The rules are in place for good reason. Let me get that out of the way first. I have a couple full conduits, they are legal but just for theory,,,, there are a couple general circuits, an equipment one and a couple lights. While bundled wire is a concern none of them really have the potential to be loaded significantly. Got a couple lights wired to a couple,, the recepts are 12 on 20 but light load and a hoist is 15a on a 10 and occasionally 20 on it for minor welding and very little of this could be fully loaded if one tried.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
If it were me, I would try to come close to the rules for an end to end conduit, even though this is just a case of protecting exposed Romex. It would make easy installation too.

Bill
 
OP
L

L5wolvesf

Well-known member
Joined
Dec 4, 2011
Messages
1,831
Location
Northern AZ
If it were me, I would try to come close to the rules for an end to end conduit, even though this is just a case of protecting exposed Romex. It would make easy installation too.

Bill

Yeah, I want to be as close to within the rules as possible.


So I looked at what I have and came up with this . . . is it OK to run 2 protective conduits into one 3 gang box? The 2 existing cables will remain as is. The additional conduit will protect the Romex for the outlet I put in that box. Later I will run an additional outlet about 5 feet further across the work bench off the new outlet. Does this sound right?

Another simple question – ha ha ha
 

arkieguide

Well-known member
Joined
Aug 10, 2017
Messages
50
You have 14/2 wg - If you have the wire why not buy some 3/4" emt run it then put one 14/2 wg into it. When you put to many wires into a pipe you run a chance of to much heat causing a fire.Yes I have seen the damage it can do.be save, in electricity safety is very important.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If you are not trying to run 2 electric heaters at max from the outlet with the light wire loaded at 15A all this doesn't mean squat. Protecting the wire from damage does. While its true that the wire has a 20 or 15 breakers it doesn't mean that's the load on them. I was eluding to that in some of my other ramble.
I got a pipe with 9 wires, 2 circuits carry 2A when all are active, 2 5A if the lights are on and one 30A wire with 15 on it for 45 seconds, one circuit could see an additional 4 1/2 grinder for few seconds, none of this makes for heat.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
None of this is like continuous process machinery, not like a commercial kitchen and even then not all those circuits are continuous or fully loaded to wire capacity and if they are there is already factor in place for derating if needed.
I put a piece of 12 in a basement convenience outlet the other day, 3 ft long down the wall, no one has used it yet and while it does technically violate fill its never going to result in a problem.
Look at the combed romex thread, only a shade from being bundled but not all these circuits will run at once, couldn't if they tried.
 