I'am replacing some 15amp (14-2) recepticales with some 20amp (12-2) in the garage attached to the house. There is two dedicated circuits, one for a fridge and one for a large freezer. Right now it is just a single circuit of 14-2. There is a section that passes through an interior wall in the house to the garage then along the wall in the garage (up 8' in 1/2"pvc) to a junction box into EMT to the plugs. My question is can I run 2 circuits of romex 12-2 in that 1/2" PVC? Comes from the panel as romex through the PVC to the junction box to EMT. The pvc is just for looks and a little protection in the garage (open at both ends, and not wet conditions)
 
To avoid these ads, REGISTER NOW!

dugger10

Well-known member
Joined
Dec 12, 2009
Messages
50
It will be tight, could work if you use some soap but I would strip the jacket off. It might pull if its a straight run and not too far.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
It will be tight, could work if you use some soap but I would strip the jacket off. It might pull if its a straight run and not too far.

Generally the wire used in Romex is not marked on the individual wires, only on the Romex jacket. Code does not allow unmarked or un-identified wire to be used, you would be violating the UL listing approvals for the Romex to do this (yes, I know, we all do this for short pigtails and jumpers, but I cannot imagine doing this with several feet of wire.

Charles
 
OP
B

blytk

New member
Joined
Nov 9, 2009
Messages
4
Location
Ontario
I tried a run of 4' with a scrap piece of 1/2" pvc and it worked good no problem pulling it. This is a straight run no bends or anything. Just what to make sure it is legal and won't cause any problems.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Generally the wire used in Romex is not marked on the individual wires, only on the Romex jacket. Code does not allow unmarked or un-identified wire to be used, you would be violating the UL listing approvals for the Romex to do this (yes, I know, we all do this for short pigtails and jumpers, but I cannot imagine doing this with several feet of wire.

Charles

Agreed, and not going to get 2-12/2 NM cables in 1/2" conduit, 3/4" will be needed.
 
To avoid these ads, REGISTER NOW!

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
use 12-3 & ground.will be better.or just a little larger 12-2-2 & ground.
 

Radar1

Member
Joined
Jan 3, 2010
Messages
15
Location
Kansas
Is the refridgerator and freezer in the same pvc that you mention? Or is the recepticle circuit in a seperate pvc? Although you may be able to fit two pieces of Romex in the 1/2 inch PVC, I would have to question the conductor fill. I belive you are not to exceed 40% of the internal area of the conduit.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
I tried a run of 4' with a scrap piece of 1/2" pvc and it worked good no problem pulling it. This is a straight run no bends or anything. Just what to make sure it is legal and won't cause any problems.

can you do it? maybe. will it work? probably. is it legal? no.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
I had a look at several CEC rules that may apply to this and came away with a lot more questions than answers,so in my opinion,no it is not likely permissable, especially if it is indeed 1/2" PVC.Rule 12-1106-PVC conduit must be protected where exposed to mechanical damage,so
one could interpret that as one can't really use it to protect NMD90!:headscrat
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
I have a question about this, same situation. Can I do 2 runs of 6-2 through 1" PVC legally?

I would have to do the calculation but i am reasonably sure that you are over the wire fill limit and the cable would have to be listed for installation in conduit.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I would have to do the calculation but i am reasonably sure that you are over the wire fill limit

There is no wire fill limit if the conduit is used for physical protection and meets the requirements of Ch. 9 Tables, Note 1.

the cable would have to be listed for installation in conduit.

Which code article requires Romex to be listed for use in conduit?
 