Romex inside Vinyl Fencing?

musgofasta

Well-known member
Joined
Aug 28, 2006
Messages
802
Location
Corona CA
I have a long run of this in my yard:

Semi-privacy-Vinyl_0.jpg


I really want to put lights on it, but NOT SOLAR. Standard decorative 120v lighting off a switch.

Is running romex inside of the vinyl fencing a really bad idea? My only alternative would be the run the wiring in conduit which would look like ****.

What (SHE) really wants is a lantern type light on every other vertical post.
 
To avoid these ads, REGISTER NOW!

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
LOW voltage . . . . only way to go.

You jerry rig some 120v and electrocute neighbor kid or dog . . . NOT good. :sad:
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Best advice is not use line voltage(120V), low voltage is best/safest way. If you do use 120V, use UF cable, not NM (Romex). The 120V will need to be GFCI protected from the source.
 

soob

Well-known member
Joined
Jul 11, 2011
Messages
551
I put deck lights on my fence. LEDs similar to this:

contemporary-stair-and-step-lights.jpg


Low voltage of course.
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
I hadn't thought of the Low Voltage route - that might work.

More money of course!

It is, but it's a bit safer :) How far is "a long run"? 12v is at a disadvantage there.

My mom has a custom-built cedar fence with 3-tier Pagoda fixtures someone installed back in probably the 70s. The fixtures were getting old, and the 120V wiring was 2 strands (red/yellow) appliance wiring stapled to the fence.

I found some really nice cast-aluminum fixtures which looked almost the same as the originals but better, will never rust, and run off 12v... looks GREAT now and perfectly safe :)
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,308
Location
Niagara Region, Ontario, Canada
I have several of these cast aluminum 12v led fixtures, they look good IMO and have a nice bright light . in 4 yrs have never had any fail other than a few bad connections underground ( has to be expected)
as mentioned 12v has major voltage loss, but because the LED draw is so little I don't think voltage drop is an issue. for fun I ran 1 off of telephone quad and there was very little drop over about 100' of wire.




51eltnieGbL._SX355_.jpg
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Romex is for dry locations only that fence is wet location.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
If you're going to use line voltage, use UF. The inside of that fence will likely see water at some point and romex is not meant to get wet.
 