I don't quite follow you. Having an unmolested neutral for the second set of receps seems to tell me that it needs to split before the GFCI so it's behaving as two branch circuits. Also, it seems to me that splitting the neutral there negates the need to pigtail the neutral at each recep because removing a device cannot break the neutral for the other leg. We're only talking 30 feet of extra neutral. Two 15-foot workstations on one leg and general convenience outlets after that.
I may just get that GFCI breaker but if splitting the neutral saves me some pigtailing then I'll do it anyway.
OP: sorry for the hijack but the shared neutral thing seems pertinent to your question regarding conduit stuffing.
U said u will be using 12/3
U can share the neutral on the line side(before) the GFCIs but U cant share a neutral between 2 GFCIs on the load side of the GFCIs meaning after the GFCIs u will need a neutral ran off of each GFCI load terminal.
This means 12/3 wont work after the GFCIs. U could use 12/2/2 instead.