Rotary phase convertor ...

1953mercury

Well-known member
Joined
Nov 25, 2012
Messages
701
Location
Steamboat Springs CO
Looking at a three phase plasma cutter that will require 60 amp/230 volt input for full capacity cutting (1"). Will my 5hp rotary phase converter be adequate for this? Thanks, Mike
 
To avoid these ads, REGISTER NOW!

A_Pmech

Well-known member
Joined
May 8, 2007
Messages
8,002
Location
IL
Looking at a three phase plasma cutter that will require 60 amp/230 volt input for full capacity cutting (1"). Will my 5hp rotary phase converter be adequate for this? Thanks, Mike

60A three-phase is about a 25 HP phase converter.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Looking at a three phase plasma cutter that will require 60 amp/230 volt input for full capacity cutting (1"). Will my 5hp rotary phase converter be adequate for this? Thanks, Mike

That will be a massive amount of power to draw from a 240 volt line... One of the reasons that the cutter was designed as three phase.

It will be interesting to see how well this works out. BTW, you're looking at about 20 KW in power there, perhaps a bit more.

One question I'd ask (I don't know the answer) is will a rotary phase converter deliver balanced power to each phase under load? I'm guessing yes, but I'm not 100% sure.
 
To avoid these ads, REGISTER NOW!

HTGTS350

Banned
Joined
Mar 2, 2010
Messages
603
I would imagine a 3 phase plasma is really only 2 phase with the fan and other addenda run off the third phase, however running something of that size from a rotary converter can't be a good idea especially seeing as a rotary converter can't efficiently make up more than 1 phase.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
I would imagine a 3 phase plasma is really only 2 phase with the fan and other addenda run off the third phase, however running something of that size from a rotary converter can't be a good idea especially seeing as a rotary converter can't efficiently make up more than 1 phase.

2 phase is a obsolete system dating back to the early days of electric power, there are some remnants of 2 phase in Philadelphia & other cities.

I have not seen welding equipment run off a RPC, but for motors a RPC is a time proven method when 3Ø is not avail.
 

bob_mp

Well-known member
Joined
Jan 7, 2011
Messages
65
Location
Bay Area, CA
I run my TIG welder (Miller Aerowave) off of my rotary phase converter; I have been doing it for more than a decade. The reason I do so is that it can produce higher currents on 3 phase (375A versus 250A for single phase). I do have a pretty good sized RPC (GWM Digi 286, which is based on a 30 HP motor).

As A_Pmech said, you will need a RPC that is much bigger than 5A to do this, but a properly sized RPC works fine for welders.

Bob
 